Gents,

I have a 3 phase 60hz 11kV syncronous induction motor, 15 years old in the North Sea.

Insulation class B
Hazardous rated Exd

I intend to do a PI test PI= R10/R1, have you any information on what DC voltage I should use for this test.

The rule of thumb appears to be 2.5kV and I note IEEE 43-2000 refers to 1kV DC for machines post 1974.

Any help/advice appreciated on what the voltage should be?

RE: Polarization testing of MV drives

I believe that would be 5kV per IEEE 43-2000

RE: Polarization testing of MV drives

I would allways recommend using a 5kV megger, and you should be looking for a PI ratio of better than 2:1 ie the 10 minute reading should be better than twice the one minute reading.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources