Shower accessability for R4 assisted living
I am working on an accessability issue for an assisted living home group R4.
I cannot find any definative proof that a shower base with a 4-inch lip cannot be used with a transfer type seat. A tub with a transfer seat is acceptable, why wouldn't a 4" lip be acceptable?
The framing and (electrical/mechanical) is too far along to economically install roll-in type shower bases.
We have looked thru the IBC, and ICC/ANSI but have not found any absolute rule.
RE: Shower accessability for R4 assisted living
Ohio Building Code 1101.2 Design. Buildings and facilities shall be designed and constructed to be accessible in accordance with this code and ADAAG.
ADAAG 4.21.7 Curbs. If provided, curbs in shower stalls 36 in by 36 in (915 mm by 915 mm) shall be no higher than 1/2 in (13 mm). Shower stalls that are 30 in by 60 in (760 mm by 1525 mm) minimum shall not have curbs.
Don Phillips
http://worthingtonengineering.com
Is the 36in. x 36in. a minimum? We have 42in. x 42in. shower bases.
If the governing authority has not adopted ADAAG; the IBC and ICC/ANSI leave a large gray area regarding this issue, could I reasonably argue that since a tub (with a 15in. + side) is permitted with a transfer type seat, therefore a shower with a 4in. curb could be utilized in the same fashion.??
I would call the local jurisidction and speak to a plans examiner or the building official. Although the 42" square requiring compliance is my interpretation, so would be the installation of either a compliant tub or a compliant shower, and not mixing of the two requirements. You logic is reasonable, but if the code is clear, the plans examiner has to enforce the code.