High Ambient 130ish deg F - 410a, 407c or 134a Question

High Ambient 130ish deg F - 410a, 407c or 134a Question

High Ambient 130ish deg F - 410a, 407c or 134a Question

(OP)
I am considering the following refrigerants for a high ambient application - replacing R-22.  This is a new design and I can select what ever refrigerant I want, so long as it is a non-ozone depleting refrigerant.

I gather R-410a is a suitable replacement for R-22 and better in performance than that of R-22 at around 95 deg F ambients.  However when the ambient starts to get-up to 130 deg F and higher, R-410a's lower critical temperature starts to lag behind R-22.

Question is - how does R-407c compare at such high temperatures and what about R-134a as it has a much higher critical temperature at 214 deg F vs R-410a at 162 deg F.

Any advice would be appreciated.

Thanks,
Bill

RE: High Ambient 130ish deg F - 410a, 407c or 134a Question

I don't know what type of equipment you are putting the refrigerant into.  New, existing, large, small or whatever?

If existing equipment, there are concerns about seal materials and compatibility.  Also each refrigerant needs to be miscible with whatever type of oil is in the system.

R134a is a good anesthesia. Other refrigerants will cause suffocation.  If you are looking at a larger system piped inside a mechanical room you need to follow the ASHRAE standard 15 for refrigeration equipment rooms.

 

RE: High Ambient 130ish deg F - 410a, 407c or 134a Question

What kind of application ?  DX ? Chilled water ?

Check with the manufacturers as well.  You may end up specifing something which may be available with only manufacturer !

For example, Carrier (to my knowledge) doesn't have R134a DX air-cooled condensing units.  

Check with them regarding the availability, specifically for the high ambient application.  Some products may be available for normal ambient, but, probably not available for high ambient application.

HVAC68

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources