3 phase 6 lead 2 speed european ac motor help
need help wiring a 2 speed motor 6 leads u v w  x y z
what configuration for low and high speeds thanks
RE: 3 phase 6 lead 2 speed european ac motor help
Try like this,
X Y Z-------Line
U V W-------Open              SLOW SPEED
U V W--------Line
X Y Z--------Join Together            HIGH SPEED
Hope this helps
is there any other configurations?
Yes, the first reply applies to constant torque application (Delta - Low speed   Wye - High speed)
If it is a constant hp application, it would be Delta - High speed and Wye - Low speed.
You need to contact the motor supplier to know which connection is applicable (is there not a nameplate on this motor that tells you how to connect it for both speeds ?)
* Women are like the police. They can have all the evidence in the world and yet they still want a confession - Chris Rock *
Hi
 your connections will depend on the type of windings in the motor....the above connections by kuldipkenya are for a motor with a tapped winding..which can be identified by a continuity test between your terminals...on this type of motor there will be a circuit between all 6 output leads!!!
 the other type is a dual wound motor with two completely seperate windings!! ie..U V W   and X Y Z  with circuits between themselves only...u-v-w   x-y-z and nothing between the two windings...
 if that is the case , it is as simple as supplying one winding or the other....leaving the other windings open.
         hope this helps
              Jeff
       www.motors-direct.co.uk