coolant/ hydraulic oil waste containment/ storage unit

coolant/ hydraulic oil waste containment/ storage unit

coolant/ hydraulic oil waste containment/ storage unit

(OP)
I am looking for some advice on waste container storage unit design. I work for a earth/ sitework and utilities contractor and was contacted by a firm who wishes to have a storage shed for the above purpose. I was told they will be dealing with coolant and hydraulic oils, and possibly pressure washing machine parts. I am aware they should probably be contacting an environmental firm and doing the whole DHEC (South Carolina)review and I don't plan on any environmental or approval process violations, but I was wondering if anyone can point me to a basic design drawing for this type of set-up. I am thinking of tanks from Myers waste oil storage system inside a containment dike accounting for 25 yr storm. What sort of design could handle where they would pressure wash into a drain? Could I sump (positive displacemnt pump)it into a water containment/recycling(separater) tank inside a fenced area? What firms make rounds to collect and dispose of captured solids or fluids. I know this is a tough question but that's why I'm in design/ construction- it never gets boring. Any help would be much appreciated.

RE: coolant/ hydraulic oil waste containment/ storage unit

Why don't you search through the federal specification? You can probably find some typical drawings there.

http://www.wbdg.org/ccb/browse_org.php?o=70

You can probably find some documents for refueling or fuel storage that may be useful, Spec Section 33.

And don't forget to design for flammable liquids.

RE: coolant/ hydraulic oil waste containment/ storage unit

I would do a couple of things.  You are on the right track with the tank and secondary containment.  I would call the oil "used oil" not "waste oil" as those are two completely different problems.  Waste is bad, surplus or recycle is good from a regulation standpoint.  See if you can get a recycler to pick it up.  If it is waste then you could contact Clean Harbors and they will pick it up.  I would also contact the state EPA guys in your area.  Ask them what they want to see.  Most of them are very reasonable and helpful.   But asking first is a completely different situation than being caught not doing it right.  

Regards
Stonecold

RE: coolant/ hydraulic oil waste containment/ storage unit

There are a lot of things to consider.  First are the appropriate regulations in your state regarding aboveground storage tanks (ASTs), for example, secondary containment volumes, release detection systems, etc.  In Florida, ASTs less than 550 gallons do not require secondary containment.  Your state most like also has a minimum cut off size.  Second are the Federal requirements.  For example, do the size of the tanks (note it is not just the size of the tanks but the total volume on site) require your client to prepare SPCC or SWPP plans?  If so, then there are some very specific requirements and best management practices (i.e. mechanisms for discharging rainwater, and loading and unloading, etc.).

Regarding the design, if secondary containment is required for the tanks it will need to contain a minimum of 110% of the tank volume plus rainwater. Check the local regs for the storm event. For this reason, some tanks and containment areas are often covered. It kind of an economic balance between cost of constructing the roof and the secondary containment size.  Lots of times, it is cheaper, safer and easier to install ASTs with built in secondary containment (see ConVaults, for an example, though I prefer metal tanks).

As for the pressure wash area, I would highly recommend adding a roof for this area and keep it separate from the ASTs.  Once they pressure wash some nasty greasy part in the area, any water (i.e. rainwater) that comes into contact with the floor and sidewalls will need to be properly disposed of.  Think of the cost of water disposal every time it rains even if they are not using the pressure washer.  If the parts are small, there are pre-fab’ part washer units that contain all the rinse waters and work really well.  If the parts are large consider using a suspended metal grate floor to stand on that way you can really slope the floor beneath to drain to a sump. Plus a grate floor will be safer to stand on.  Most likely you will not need to install a pump in the sump, just provide access for vacuum truck which is how most of these kinds of water are collected. Also ask the client if they plan to use any solvents, you will need to check the chemical compatibility with you tanks and construction materials.

Finally MAKE SURE YOU SEAL THE FLOOR and SUMP!! I cannot tell you how many sites I have been to that floor and/or sump was not sealed and the soils and groundwater beneath the site were contaminated due to poor construction and/or design.

Sorry if I ramble on to much, I am new to the forum.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources