PRV valve pressure drop
I'm in need of some assistance in calculating some flow vs pressure specifications, in order to make some changes to the system.
I have a PRV valve that has a preset setting of:
PRV NO.1 & 2 SET PRESSURE = 1034 KPA (150 PSI) @ 0.63 L/S (10 USGPM)
Meanwhile the design criteria states the output to be:
PRV NO.1 & 2 OUTLET = 683 KPA (99 PSIG) @ 33 L/S (520 USGPM)
                    = 1034 KPA (150 PSIG) @ 0.63 L/S (10 USGPM)
I'm having difficulty determining or verifying the calculation that will prove that the flow @ 520 USGPM will yield a pressure drop to 99 PSIG, which equals 10 USGPM @ 150 PSIG in this 4" system.
Something just seems odd and I've tried a number of different formula's, obviously not the correct one. I'm hoping to understand what calculation was done, and conduct it again for a flow of 400 USGPM.
The valve is a FORD 4" PRV.
Any help would be appreciated.
RE: PRV valve pressure drop
The basic equation for liquid flow across a partially open valve is,
Q = Cv (ρ/ρb) * (δP)  *ρw/ρ)^0.5
Q = flowrate at STP conditions
ρ = density of product at flow conditions
ρw = density of water
ρb = density of product at STP
δP = pressure drop across the valve
Cv = Valve Coefficient at a given percent open.
Did that help?
http://virtualpipeline.spaces.msn.com
"What gets us into trouble is not what we don't know, its what we know for sure" - Mark Twain