Cooling Tower Water

Cooling Tower Water

Cooling Tower Water

(OP)
Is it absolutely necessary to use softened water in cooling towers? What is the maximum hardness of water that may be used as cooling tower water?

RE: Cooling Tower Water

olmedo:

No, it is not "absolutely" necessary to use softened water in a cooling tower. What is fairly necessary is to consult a well-known water treating company and ask their advice based on your raw water composition as to:

(1) The number of concentration cycles to used in the system
(2) The proper water treating chemicals and the proper amounts of those chemicals to be used for scale control, anti-fungus control, pH control, etc.

The Nalco company and the GE Betz company are two of the well-known experts in this field.

Milton Beychok
(Visit me at www.air-dispersion.com)
.

RE: Cooling Tower Water

olmedo,
The cleaner the water you are using, the longer you can circulate it in your coling tower. The dirtier, more of it has to be blown-down to be acceptable for a particular cooling tower you purchased, more make-up has to be pumped in the system, to not mention the hasless of disposing off the contaminated water. Also, the local chemicals you have to use will cost you more. In other words, you trade the less treated water for additional costs related to the use of untreated water. Obviously, you are the only one to judge it to suit your budget and the plant circumstances. You should consult the cooling tower fabricator for his recommandations also.
gr2vessels

RE: Cooling Tower Water

In most cases, completely softened water will cause corrosion in condenser, basin and cooling tower/exchanger.
Depending from raw water composition and treatment program, you can operate up to Ca levels of 1100mg/l as CaCO3 (i.e Palo Verde circulating water analysis).
Two listed in previous post companies should give you good answers what you can do with your water.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources