fault calculation

fault calculation

fault calculation

(OP)
Is it true to say that given the 3 phase short circuit fault current at a certain point in a system, that a fault between two phases only will produce 0.865 times the 3 phase current value in those two phases ?

RE: fault calculation

    It is fairley true when fault is located far enough from a generator. In other terms, when impedances for positive and negative sequences are equal, then the statement is right (.866 instead .865, (sqrt3)/2)

Julian

RE: fault calculation

(OP)
Many Thanks Julian,

kvkev

RE: fault calculation

Comment: The above postings may need a little clarification, e.g.
Iline-line = [(sqrt3)/2] x Ithree-phase = 0.866 x Ithree-phase
This can obviously be further elaborated on.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources