Control Transformer circuit
|
Control Transformer circuitControl Transformer circuit(OP)
How can I explain what actually happens when opening a CT circuit under load, which generates excessive high current and high transient voltages.
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
|
RE: Control Transformer circuit
The primary of the CT is in series with the power circuit being measured. The current in the secondary of the CT is proportional to the current in the primary. The CT secondary will generate enough voltage to cause the secondary current to flow or it will saturate trying. Prior to saturation, and even into saturation, extremely high voltages can be developed across the open secondary, often leading to flash over.
RE: Control Transformer circuit
Lethal voltages..
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Control Transformer circuit
The secondary of the CT knows one thing, "I need to produce X Amps (Usually 5A)", based on the resistance of the secondary circuit it will produce the necessary voltage to maintain that current flow. Under normal conditions the resistance is only a few ohms, so only a few volts is necessary, if you lift the leads (Open the circuit) the resistance incleases as you pull the lead away, the voltage increases, and you will draw an arc. Then I show the interlocks and shorting block/contacts for a 50/51 relay (Hands on, pass around the class).
Not 100% acurate but gets the point and basic theory across, I would use a different one for Engineers and another one for intro students.
RE: Control Transformer circuit
I take a little different tack with the explanation to technicians.
"If I have a transformer with ten primary turns and ten secondary turns and I put a volt in the primary, what's the secondary voltage?"
"Now, if I have a transformer with ten primary turns and and TWENTY secondary turns and I put a volt int he primary, what's the voltage on the secondary?"
"Now, if I have ONE primary turn and 120 secondary turns, and I put 4160 volts on the primary, what do you think the secondary voltage will it TRY to produce?"
Yes, it bends the reality just a little bit, but most techs get the idea...
old field guy
RE: Control Transformer circuit
The CT has to produce enough voltage across the secondary winding to create a current flow in the proper ratio to the primary current. As the burden of the secondary circuit increases, the voltage required to produce the same current increases.
The higher the secondary circuit impedance, the more voltage, so if you open the secondary side, impedance goes to infinity and the voltage tries to go to infinity as well.
RE: Control Transformer circuit
"The electroician said that the last thing he saw was a big orange basket ball!"
In the rest of the course he often reminded us of
"The big orange basket ball."
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Control Transformer circuit
The transformer we were commissioning was the replacement for one which blew up 11 months earlier killing three of our friends so at the slightest hint of a problem we ran like hell. Looking back it was slightly irrational but we were terrified when that CT circuit lit up. There was no big bang or any other huge drama but the terminals were in a real mess and about 3" of conductor was missing, just completely gone. It wasn't even a field crimp, it was wrong when it left the factory.
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: Control Transformer circuit
I was, however, a bit surprised to see the heading "Control Transformer circuit". A control transformer is NOT a CT. CT is reserved for use with Current Transformers. And Current transformers are what the answers are about.
Opening the secondary of a Control Transformer is absolutely non-critcal. Please, Pup7, do not create confusion bu telling your pupils that they are not supposed to open the secondary of a Control Transformer - and DO NOT tell them to keep the secondary of it shorted. That is not good at all.
Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
RE: Control Transformer circuit
A "Control Transformer" is better described as a Control Power Transformer abbreviated CPT so as to avoid this very confusion. The term "CT" is reserved for Current Transformer, and THAT is the one you should never open the circuit on. No problem opening the circuit on a CPT!
CPT
CT
RE: Control Transformer circuit
I shall be more careful next time
Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
RE: Control Transformer circuit
RE: Control Transformer circuit
RE: Control Transformer circuit