Shearwall-steel frame lateral connection

Shearwall-steel frame lateral connection

Shearwall-steel frame lateral connection

(OP)
I have a 5-story dual system building where the gravity loads are supported by steel frame, and the lateral loads are resisted by cmu shear walls.  I have a question regarding the connection between these two systems, however.  

I need a connection that will lateraly brace the cmu wall at each floor and transfer lateral load from the steel frame (with concrete-on-metal deck diaphragm) to the cmu shear wall, but not transfer any vertical load from the steel frame into the cmu wall.  Does anyone have an idea for a detail or product that can accomodate this connection?  Thanks.

RE: Shearwall-steel frame lateral connection

First, your structure would not be considered a "dual system".  A dual system uses stiff lateral elements (shear walls, braced frames) in combination with a backup system of moment-resisting frames.

The connection to the shear walls could be like a ledger angle or channel but with anchor bolts in vertically slotted holes so that the gravity load is not transferred to the wall.

RE: Shearwall-steel frame lateral connection

I agree with Taro.

Use a Tee section (leg vertical) with Nelson stud anchors embedded into the top of the CMU wall and a vertical fin plate welded to the bottom of the WF beam.  Connecting the plates with the bolts with a vertically slotted hole system will get you where you want to go.  

You could also use a channel with Nelson studs, flanges down, with a fin plate welded to the top to catch the fin plate from the WF beam as Taro suggested.

Mike McCann
McCann Engineering

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources