200 amp Distribution panel in Boiler Room

200 amp Distribution panel in Boiler Room

200 amp Distribution panel in Boiler Room

(OP)
Can a 200 amp distribution panel be located in a boiler room?  The room will not get hotter than max 120-deg F.
thanks,

RE: 200 amp Distribution panel in Boiler Room

1.  Electrical panel requires a dedicated space including space above it.  See NEC 110.26.  

2.  Ambient temp of 120 deg F would require de-rating of all the breakers in the panelboard and panel bus rating.  Panelboards built to UL and NEMA standards are rated for a maximum ambient of 40 deg C, which is 104 deg F.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources