SOG Shear Reinforcing Under Wall
5

SOG Shear Reinforcing Under Wall

SOG Shear Reinforcing Under Wall

(OP)
I am hoping someone can point me in the right direcion.  I am looking for recommended shear reinforcing details for a slab-on-grade with a heavily loaded wall.  Going thicker with the slab is not a practical option at this point and was wondering if there are any references out there that specifically address this situation.  I can find lot with suspended slabs but nothing that seems specific to a slab on grade.  Is this not a recommended practice?  Particularly if the slab needs to remain water tight?  I am currntly entertaining the idea of a "U" or "Z" sirrup but the spacing is going to need to be pretty tight.

I appreciate any thoughts you may have.

Thanks,

waytsh

RE: SOG Shear Reinforcing Under Wall

Put in a thickened footing or separate footing under the wall.

Refer to "Designing Floor Slabs on Grade" by Ringo and Anderson.

RE: SOG Shear Reinforcing Under Wall

Consider strips of shear studs like those used on elevated slabs supported at columns. If you turn your problem upside down, the loading is very similar: a distributed load on the slab (soil reaction) and a point support (wall load).

A more desirable solution would be to install a thicker footing designed for the wall, but it sounds like the slab base, reinforcing, and wall forms are already in place (?).

RE: SOG Shear Reinforcing Under Wall

Don't forget that ACI 318, section 15.7 states that the minimum footing thickness is based on a minimum depth to rebar, d = 6".

So with 3" cover you have about a 10" slab minimum.

RE: SOG Shear Reinforcing Under Wall

(OP)
My slab is currently a uniform 15" thick.  It does not make sense to me but the owner and contractor insist that it is going to be much cheaper for them to install the shear stirrups instead of just thickening the slab.  I have considered the shear studs and may go with them if there is not a good reason for avoiding shear reinforcing.  Maybe the owner and contractor will then realize just how expensive this shear reinforcing is going to be.

RE: SOG Shear Reinforcing Under Wall

The wall is bearing on the slab on grade and is supported by granular fill?  Can you place a concrete pour under the SOG in the vicinity of the wall?  Should be inexpensive just a matter of excavating, compacting and placing concrete... what is the consequence of the slab cracking?  Is it worth the risk? even with large amounts of steel, the slab can still crack.

Can the wall width be increased? a small pedestal?  Is the problem beam shear? or punching shear?  Can you use shear friction? with large bars? a recent project has 35M@6"

RE: SOG Shear Reinforcing Under Wall

A 15" thick slab ought to be able to support alot of load. How much load are we talking about? Joint locations?

I assume it already has top and bottom reinforcing. How much reinforcing? Are you sure you need shear reinforcing?

What is the soil modulus?

RE: SOG Shear Reinforcing Under Wall

(OP)
dik, thanks for the suggestions.  The wall is precast so unfortunately I can not go any thicker than what it already is.  The problem is punching shear.  I had thought about shear friction since I will have a substantial amount of flexural reinforcing under the wall.  I didn’t think I could “double dip” on the reinforcing if it is already being used to resist flexure…or are you suggesting additional reinforcing specific to that purpose?

Maybe I better mention my analysis approach as well in case that is flawed.  I have analyzed the slab on STAADPro because of the complexity of the loading and the wall system.  For my worst case load combination I am getting a shear stress under my wall of 108.2 psi.  Which translates to about 19.5 k/ft.  which I am then checking against ACI 318 Eq. 11-3 or 11-5.  For my model I used a uniform thickness of 15” but in reality the slab is only 12” thick under the wall because of the keyway.  So my d is approximately 8.5.  My concrete is 4,000 psi so I am getting an allowable shear strength of 9.68 k/ft for a one foot wide section.

Is this a rational approach or am I oversimplifying?

Thanks,

waytsh

RE: SOG Shear Reinforcing Under Wall

(OP)
sorry jike, you posted as i was writing and I didn't notice before submitting.  The unfactored load from that particular wall is DL = 10.5 k/ft and LL = 13.9 k/ft.  The wall is 14" thick.  I will have top and bottom mats in the slab under the wall.  It is going to be #5 bar @ 8" o.c. but I may need to change the bottom mat to something like #9 bar @ 4" o.c. to meet the flexural requirements.  i haven't determined what I am going to do there yet.

RE: SOG Shear Reinforcing Under Wall

(OP)
soil modulus = 90 pci

RE: SOG Shear Reinforcing Under Wall

Sounds like you did a beam on elastic foundation analysis.

Is there any way to increase the concrete strength?
or
Is there any way to eliminate the keyway?

RE: SOG Shear Reinforcing Under Wall

(OP)
I can increase the concrete strength but i don't think it is going to get me to where I need to be.

I need to keep the keyway since it is integral to locking the base of the precast panel in place and the grout and sealent help make it a nice watertight connection.  Any connection that would sit above the slab I do not think would perform as well.

Thank you for the suggestions.

RE: SOG Shear Reinforcing Under Wall

I think shear friction is the solution.  However, I wouldn't use the reinforcing near the slab face to provide shear friction. I don't believe bars near the face of a slab falls under "where it is approporiate to consider shear transfer across a given plane" verbiage of ACI 11.7.1.  I'm sure others disagree.  I would add additional shear friction bars at the mid-depth of the slab.  You're not talking about a lot of reinforcing, as you only need to reinforce for the shear in excess of the slab capacity.

RE: SOG Shear Reinforcing Under Wall

Design it as a strut and tie.

Provide enough reinforcement in the bottom to resist the triangulated forces. Then, like a truss, there is no shear only axial forces.

PS: a 15" slab! are they wheeling the titanic around on this?

RE: SOG Shear Reinforcing Under Wall

As for shear friction, additional... it's more efficient.  Because reinforcing for shear friction is generally developed in tension... it should be additional As and not included in the flexural component... unless you have added steel for compression and the bar is in the right face.

miecz:
If the load is from the top, then top bars are proper for shear friction... it's a matter of tearing the top bars through the slab for failure to occur.

Dik

RE: SOG Shear Reinforcing Under Wall

Forgot to add... you might consider that all the load is transferred by the outer 1/4 parts of the wall... this will bump the shear up a tad.

The reasoning being that the slab will flex under load and if you had dowels in the middle portion of the wall, they would likely be in tension.  Your FE model likely reflects this...

Depending on your lateral load at the base of the wall, a 2x4 key should be sufficient and will have little effect on the shear or flexural capacity... you may be able to use the full slab depth for calculating d.

Dik

RE: SOG Shear Reinforcing Under Wall

dik

You're right, the top reinforcing is proper for shear friction, in this case.

RE: SOG Shear Reinforcing Under Wall

(OP)
Good news.  As it turns out the owner and contractor are now willing to thicken the slab.  However, I am still interested in discussing this further for future projects.

My top bars in this location are only serving to meet the temp. and shrink. requirements of ACI 350 and are not flexural resisting steel.  So if I am understanding everyones opinion correctlty it sounds like I could use the top bars as my shear friction bars since they are not providing flexural strength.

Would you be of the opinion that this is as good as thickening the slab?  If so I could save the owner some time and money since they will need to bring excavating equipment back out to the site to trench out the thickened area under the wall.

I am also curious what you think about the way I evaluated the STAAD data.  Does this seem reasonable?  Is there a better approach?

RE: SOG Shear Reinforcing Under Wall

On second thought, I'm going to back off on the use of top bars.  I agree that they are effective for shear friction reinforcing at the failure plane in line with the face of the wall. However, there are other potential failure planes at some small distance away from the wall where the top bar may spall the concrete.  The shear at these locations is still quite high and difficult to determine.  I would just play it safe here and add reinforcing at the middle of the slab.  I would extend it away from the wall to the point where the concrete can handle the shear on it's own, but no less than the development length.

RE: SOG Shear Reinforcing Under Wall

As is usual with shear friction, no two people agree on exactly how it works.  To me, it is just desperation.  The slab should be either be thickened to take the shear or proper shear reinforcement used.  By the way, this is a line load, so the shear is beam shear, not punching shear.

RE: SOG Shear Reinforcing Under Wall

Hokie66 is right. Check previous threads on shear friction; you'll see a wide variety of opinion.  If I understood correctly, many engineers would use the bottom flexural reinforcing for shear friction, allowing it to do double duty.  I'm not in that camp.

Also, strike that remark I made about reinforcing for the shear in excess of the slab capacity (What was I thinking?).  Shear friction reinforcing would need to need to provide for the total design shear at the failure plane.

RE: SOG Shear Reinforcing Under Wall

I tend to think that shear friction works by putting the rebar into tension... and I consider it being additive... AISC for anchor rods also adds the shear force in the rod to the developed tension... I think that if you are using rebar for both the shear friction and tension, you could be looking at a failure...

Dik

RE: SOG Shear Reinforcing Under Wall

(OP)
I would agree that the tension bars should not be considered for shear friction.  To be honest the more I think about it am a little reluctant to use any shear friction in this situation.  When you run the numbers it gives a very high shear capacity.  If all this shear capacity is really there from shear friction then why isn't this method mentioned as a shear reinforcing option for suspended slabs or even beams?  I can understand how a beam will still need some confinement, but using this method you could greatly increase your stirrup spacing.  I'm just wondering if it is not mentioned because testing has shown it is not a viable solution or if the code guys just didn't feel like tackling the topic.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources