Grounding of IT Equipment Branch Circuits

Grounding of IT Equipment Branch Circuits

Grounding of IT Equipment Branch Circuits

(OP)
I searched on this, but didn't find a real answer.  If I run multiple circuits in the same conduit, and my practice is to run an insulated ground with the phase conductors, should I be running multiple ground conductors.  Some references say YES. I personally think it's overkill. Any opinions.

As an example, I am running 4 - 208v, 1phase,30A services in a single conduit(derated as necessary). My design engineers want to run 4 separate ground conductors in the conduit.

RE: Grounding of IT Equipment Branch Circuits

250.122(C) in the NEC permits the use of a single equipment grounding conductor.  It would be sized based on the largest overcurrent protective device for the ungrounded conductors in the raceway.  Note, this assumes that you are asking about the equipment grounding conductor and not the grounded (neutral) conductor.

RE: Grounding of IT Equipment Branch Circuits

(OP)
Yes, I am referring to the grounding conductor.  I know NEC allows it. I was asking more if this is done from an IT equipment noise standpoint.

RE: Grounding of IT Equipment Branch Circuits

IT eqpt has "typical type corcom" filters in it that bleed current to ground.
Racks and racks of eqpt can add up to sometimes a couple of amps returning on the ground.
This creates an IR drop and voltage potential differences between racks.
Signal grounds between eqpt. will now have current flow and thus possible signal contamination (noise).

The lower you can keep the ground impedance.the smaller is this IR drop.Therefore,yes the more parallel grounds is better(lower impedance).

RE: Grounding of IT Equipment Branch Circuits

Ghostbuster,

Thank you for the information. Are corcom filters used in the server room equipment? Does all IT equipment provided with corcom filters?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources