By definition cross-ties must alternate ends when placed.  Ref ACI-318.

In columns that have ties with seismic hooks, is there a requirement for these ties to be alternated?  Or is the alternating of ties engineer’s preference and if so this preference is based on what criteria?

RE: column ties - when to alternate ?

See section 21.4.4.1.  Crossties (135 degree hook on one end and 90 degree hook on the other end) must be alternated.  But hoops with all 135 degree hooks are not required to be alternated.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources