Cable Protection - Protecting Shield Wire from a Ground Fault?

Cable Protection - Protecting Shield Wire from a Ground Fault?

Cable Protection - Protecting Shield Wire from a Ground Fault?

(OP)
Protection Guru,

When checking 34.5kV feeder relay ground element settings for cable protection, is it necessary to consider protecting a cable from a feeder ground fault with all the ground fault current returned via the shield wire (1/3 netural)?

Thank you,
Best Regards,
Bing

RE: Cable Protection - Protecting Shield Wire from a Ground Fault?

You need to be concerned about the short-time thermal rating of the shield.  Even with a separate external ground wire, the shield will carry a lot of current during ground faults.  It's generally not a big problem.  Okonite has data on this in their cable handbook, IIRC.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources