shear blocking trusses
We are in the process of re-vamping our shearwall details. The detailing of shear blocking trusses used when floor trusses are perpendicular to the shearwall on both sides is causing a discussion in our office. Can anyone elaborate on how you detail shear blocking trusses, and how you fasten them to the truss? Thank you.
RE: shear blocking trusses
In that situation, I run the wall double top plate about 1/4" or so below the bottom chord of the trusses (depending on the max deflection of the trusses) and use Simpson DTC clips to transfer the shear from the blocking to a 3X flat nailer attached to the floor/roof diaphragm above. The DTC clips allow vertical movement, but not lateral, so lateral load is able to be transmitted.
All connection frequencies and nailing will obviously depend on the load seen.
Mike McCann
McCann Engineering
Sometimes - in smaller apps - the Simpson H10 or similiar will suffice w/o blocking.
In seismic areas - 2x blocking is usually required.
Alternatively, what you can do is create a collector element (like what MiketheEngineer suggests) and identify a few areas along the shearwall to create a blocking system or panel that can take all the shear instead of sheathing up between each and every truss.
I have also seen short sections of floor truss between floor trusses when they were very tall - say 24'' and then sheathed with plywood.
You need to develope a "chord" of some sort on the edges of the floor or roof diaphragm. Don't forget to detail the splices.