Hello all,

What shall be the criterias for maximum allowable span for vertical piping.

Is it same for horizontal piping criterias.

thanks in advance

saliba

RE: span for vertical piping

(OP)
Dear David,

Thank you for your reply,

But I guess the values shown  in the  are for horizontal piping.

What I ask is it the same for vertical piping. is there any constraints other than for horizontal piping.

RE: span for vertical piping

saliba11

It is really NOT that simple.  

Hanger spacing charts for horizontal "runs" of pipe are based upon limiting the bending stress in the horizontal piping (and they DO NOT address concentrated loads like large valves).  Supporting vertical piping is quite a different thing.

How a vertical riser is supported depends greatly upon its operating temperature.  If you support the "hot" riser near its top, the pipe will expand down its length so that the total expansion displacement at the bottom of the riser may make the rest of the support scheme difficult to design.  Similarly, the opposite situation is to be expected if you were to support the riser too close to its bottom.  If there is rotating equipment to consider the expansion of a long riser may require some "creative" design work.

Generally, you will want to support the riser as near to its top as is practical (if rotating equipment is not an issue) so that the weight of the vertical piping will cause a tensile loading in the pipe wall.  Compressive vertical loadings in pipe risers that are supported at their bottom tend to cause column buckling loadings (instability) in the vertical piping.

In some long vertical risers in power plants (main steam, hot reheat, cold reheat, etc.) you will see the piping supported by a "rigid" rod hanger pair somewhere near the "midpoint".  Then there will be spring hangers above the "rigid" location (elevation) and also be spring hangers below the "rigid" location (elevation).  The height on the riser where the "rigid" rod hanger is located will be at about the same elevation as the point where the piping terminates at the connection to the turbine.

Pipe support design includes equal shares of science and art.  Our good fortune is that we are now blessed with computers.

You may benefit from the knowledge that Anvil-Grinnell has a FREE hanger design manual available that will give you a lot of design background and some valuable design data.  You can download it here:

http://www.anvilintl.com/db/catalogs/Pipe_Hanger_Design-05.pdf

Regards, John.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources