Wind farm step up transformer

Wind farm step up transformer

Wind farm step up transformer

(OP)
Any one knows why there are tertiary delta winding used in wind farm substations? For harmonic cancellation or kVAr compensation? It seems to me that the PF regulation is done on the LV side of the same transformer which is 25kV or 34.5 kV. Seems to me this is mainly for harmonic cancellation. The HV side of the same transformer is (usually 138 kV) solidly grounded and the LV side is resistor grounded.
Comments are appreciated
Regards

RE: Wind farm step up transformer

A tertiary delta is sometimes used on YY transformers to provide low impedance zero sequence current shunt. It also provides what amounts to a short circuit for 3rd harmonics.

See thread238-130030: Buried Delta tertiary- Zero Sequnce

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources