Grounding in conduit
Grounding in conduit
(OP)
Say you have 4000amp feeder breaker feeding 4 conduit sets of three 500mcm cables at 34.5KV on a 800 ft run (lets assume pvc buried 6 ft in the ground). So, we have 4 conduit runs with three 500mcm cables per conduit.
My question is what size grounding cable does the NEC require to run in each conduit?
My question is what size grounding cable does the NEC require to run in each conduit?
Be Safe.






RE: Grounding in conduit
But a 4000A C/B at 34.5kV? That's almost 250MVA.
And four 500kcmil/phase? Per NEC T310.78, three circuits of 500kcmil at 35kV is good for 315A.
RE: Grounding in conduit
It is actually twelve 500kcmil/phase. Need current carrying capacity for over 3000amps.
Be Safe.
RE: Grounding in conduit
Will all due respect, this type of system is usually designed by a professional engineer who wouldn't be asking these questions. This is basic NEC which an electrician should be familiar with, also.
RE: Grounding in conduit
Now, lets say we are splitting that through 4 conduits (because of the cables current carrying capacity). Do we still need 500 kcmil/conduit? and if so why?
Be Safe.
RE: Grounding in conduit
RE: Grounding in conduit
RE: Grounding in conduit
I have concluded that I would be in violation if I did not have a minimum of one 500 kcmil ground conductor/conduit in this application.
However, I dont think this is the common practice. I have come across engineering firms that often do not even run ground wire in conduit. They put one ground wire in a seperate conduit & a ground wire outside the duct bank or concrete. Then tie them together with the ground shields at the terminations.
Be Safe.
RE: Grounding in conduit
RE: Grounding in conduit
Be Safe.
RE: Grounding in conduit
RE: Grounding in conduit
Whether allowed or not (there used to be some limit on using larger conduits for grounding conductor) I would NOT choose to utilize conduit as ground return path for such circuits. One missing conduit fitting could result in a tragic transfered potential.
RE: Grounding in conduit
I'm also wondering about running 800ft with 4000 amps. If it is underground, thermal derating may be a significant consideration as well.
RE: Grounding in conduit
One issue is how do you tie together 12 500 kcmil grounds and what does it do for if the equipment ground is a 4/0 anyways?
hmm...
Be Safe.
RE: Grounding in conduit
I would also expect the equipment this terminates at to have a ground bus or ground plate capable of accepting that many terminations. Don't confuse the ground electrode conductor with the equipment ground conductor.
As others have said, and with all due respect, this should be calculated by dedicated professional study. This is more dangerous than playing with dynamite.
RE: Grounding in conduit
Electic:
Actually there is not a ground bus or ground plate for the terminations, but shortly it will be installed :)
If interested here is some general info about the duct:
18 - 6" pvc conduits - arranged 3 high and 6 wide. The 2 columns in the middle are ran due to spacing required between the cables to minimize heating also could be used for future expansion.
In each conduit will be 4 - 500 kcmil (1/phase and 1 for the gnd)
The spacing will require 10" off center between each column to minimize the heating and cable will fill the 2 end columns. Rows offset 15". The hottest cables will be the bottom inside cables.
The current capacity will be 300amps allowing for about 3,600 amps through the feed, but future expansion expects to pull 3 more 500 kcmil dropping it to 272 amps which gets you just over 4000 amps total.
Thanks everyone.
Be Safe.
RE: Grounding in conduit
The 2008 NEC requires equipment grounding conductors to be "contained within the same raceway, cable, or otherwise run with the circuit conductors". It has been common practice to install a single ground with the duct bank either loose or in a separate duct. The fact that this has been accepted is supported by some of the duct bank figures such as Figure B.310.3 (annex B) which shows the separate ground where each phase conductor is in a separate duct.
The way I read the 2008 NEC you need 500 kCMIL either way.
RE: Grounding in conduit
Comments appreciated.
Be Safe.
RE: Grounding in conduit
RE: Grounding in conduit
1. A bonding conductor in each nonmetallic raceway. – Rule 10-404 (2).
2. According to CEC rule 10-814(3) “The bonding conductor shall be permitted to be paralleled but shall not be smaller than that determined by dividing the rating or setting of the overcurrent device by the number of bonding conductors and selecting from table 16 (in the CEC) a conductor size to satisfy this result.”
3. So, 4000 Amperes / 12 conduits = 333.3 Amperes. Table 16 indicates a #3 AWG copper wire would be required in each conduit.
I have to qualify the above by stating that this is a very unusual conduit/cable configuration. Transferring a large amount of electrical energy in this manner is could be problematic in a number of respects. Ensuring equal current flow through all these parallel conductors may prove challenging. Terminating and bracing this number of conductors in a switchgear enclosure of some type may also be interesting/impossible. I would review this design very carefully prior to proceeding.
RE: Grounding in conduit
RE: Grounding in conduit
I assure you it is challenging but very possible.
I have a new question:
We have a resistance grounded neutral that limits ground fault to 1200 amps. So Im thinking we should use that for sizing the ground cable rather than the 4000 amps of the breaker rating? The grounding grid of the substation is sized for 1200 amps rather than 4000. Are their provisions in the code for this? Considering "common practice" what would you guys do?
Thanks.
Be Safe.
RE: Grounding in conduit
There are no provisions (that I am aware of anyway) for this type of logic in the Canadian Electrical Code. The size of the bonding conductor is determined by the rating or setting of the overcurrent device ahead of the equipment without consideration for the type of system grounding that may be used.
"Considering "common practice" what would you guys do?"
If this system really has to be installed as you have described I would, at a minimum, specify that one #3 AWG copper bonding conductor be installed in each conduit that contains ungrounded circuit conductors as per my previous post.
RE: Grounding in conduit
RE: Grounding in conduit
Be Safe.