I'm looking for what is considered best practice as far as referencing the negative (common) side of a 24VDC instrument power system to ground.
This is the instrument power (not signal) for 4-wire transmitters (not loop powered transmitters).
Are there any pros / cons to doing it?
My thought was that it would be safer as voltages in the field would be sure not to float above 24V, but my staff tell me that they are worried of shorting out instruments if the + is accidentally grounded during maintenance.

Any IEEE or other references on this?

Thanks in advanced,
Jan T.

RE: Instrument Power 0VDC Referenced to Ground?

We tend to tie the common side to ground through a parallel resistor and capacitor.  R = 1Mohm, C = .01 uF.

RE: Instrument Power 0VDC Referenced to Ground?

(OP)
Thanks Henneshoe. Any reason you do it this way?
Any Pros / Cons for floating the 24VDC vs grounding it?

RE: Instrument Power 0VDC Referenced to Ground?

Floating it may cause electrostatic build-up with subsequent (sometimes interfering) discharges to ground. So, a "leak" to ground is good to have. The capacitor is good to short high-frequency interference to ground. Often, the 0.1 uF capacitor gets a ceramic HF capacitor in parallel.

Sometimes, it is good to "ground everything everywhere". But that does not seem to be the first choice in instrumentation. More so in automation and drive applications.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources