analog differential or single ended inputs
I am wiring four 4-20 mA inputs to a control logix 1759 AI8 module, via IFM module. All four inputs are from 4 wire transmitters, supplying their own power. I have two options,
1. Wire the card as differential analog inputs giving me no spare inputs.
2. Wire the card as single ended inputs, giving me 50% spare capacity.
I am leaning towards option 2, my uncertainty is having the commons all tied together (single ended input). Is this a problem if all the 4-20 transmitters are isolated? I think not but am a little unsure. Thank's for any response. Steve
RE: analog differential or single ended inputs
Well since 4-20 makes no direct sense to differential are you really converting the 4-20 with a resistor across it?
If yes. I'd go with single ended. Just don't do anything that would prevent you from going to double ended if some hitch comes up.
With your isolated 4-20 I think you're good.
Keith Cress
If the four 4-20 lines are insulated from any potential, including gnd, AND have separate power supplies AND are not used for any other purposes where they may also be connected to gnd or some other potential, then you can use single ended connection to your IFM module.
What you describe seems to be exactly such a system, so just do it.
Gunnar Englund
www.gke.org
Good morning Keith! Yes, of course, a resistor is needed.
Gunnar Englund
www.gke.org
Thanks Keith,
The analog current input card has internal 249ohm resisors, so the card does the conversion to 1-5 Volts.
Steve