Allowable Stress in Shell at Anchor Attachment
Question 1) Shouldn't the heading of the right-most column of Table 5-21b read "Allowable Shell Stress at Anchor Attachment" (as Table 5-21a reads)?
Question 2) The allowable shell stress at anchor attachment is given in Table 5-21b as 25,000 psi which is lower than the values listed for many of the materials listed in Table 5-2. Is this correct?
Question 3) Shouldn't the allowable stress for the combined loads of Design Pressure + Wind be higher? For instance, the ASME code Section VIII-div.1 allows a 20% increase in allowable stress when combining wind or seismic loading with other loads.
RE: Allowable Stress in Shell at Anchor Attachment
Joe Tank
Joe Tank
"Chair height must be high enough to distribute anchor bolt load to shell.. without overstressing it."
"Except for the case where a continous ring is used at the top of the chairs, maximum stress occurs in the vertical direction, and is a combination of bending plus direct stress."
"Maximum recommended stress is 25 KSI. This is a local stress occurring just above the top of the chair. Since it diminishes rapidly away from the chair, a higher than normal stress is justified, but an increase for temporary loads, such as earthquake or wind is not recommended."
This is based on work of P.P. Bjilaard, "Stresses from Local Loadings in Cylindrical Pressure Vessels", ASME Transactions, Vol. 77, No. 6, 1955
If the calculated stress due to anchoring is up around 25,000 psi and if the additional stress due to pressure, static head, etc, is also up near the maximum allowable stress per Table 5-2, the case could arise where the stress is well above the yield point of the material. I'm having trouble following your logic.
Joe Tank