Shear wall designed for certain ductility say Rd=2 and R0=1.4 has to have a foundation system designed for the forces resulted from lateral loads but using Rd=1.0 and R0=1.0, which is 2.8 times the forces that could be applied by the wall. My question is: if these full forces will never transfer to the foundation because the wall will start going through the plastic range at lower loads, then why foundations have to be designed for full loads. I understand that the foundation system has to stay intact while the structure is going through the ductile behavior, but that could be achieved by magnifying the forces due Rd=2 and R0=1.4 by 10% or 20 % not 280%.

RE: Design forces for foundations of shear walls

How do you know 10% or 20% is sufficient?

RE: Design forces for foundations of shear walls

(OP)
UcfSE,
Thanks for you question. What I don't understand is why the foundation system has to be designed for much higher loads than what the wall will be capable of transfering to it.

RE: Design forces for foundations of shear walls

That's capacity design...you should protect "weak" elements who don't possess ductility.
There is a clause in Eurocode 8 which "overcome" your problem...you just multiplied the forces (with included ductility factor, i.e. 2.8) with 1.4. That basically means that you account with ductility 2.8/1.4=2 in designing your foundation.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources