Determining Transformer Resistance & Reactance

Determining Transformer Resistance & Reactance

Determining Transformer Resistance & Reactance

(OP)
Given the following test data:
Transformer base rating (in VA)
Transformer no-load (or iron) losses (in W)
Transformer load (or copper) losses (in W)
Transformer percent impedance (%Z)

How do you determine %X & %R values?

some confusion on my part...is it:

a) load losses/rating x 100 = %R

or

b) (no-load losses + load losses)/rating x 100 = %R

or some other way entirely?

The rest is then easy given %Z = SQRT(%X^2 + %R^2)

RE: Determining Transformer Resistance & Reactance

Version a) of your formulas is closest to the the correct one:

SQRT(load losses/rating)=%R

RE: Determining Transformer Resistance & Reactance

It is not possible to correctly identify %R and %X from the data you have provided.

However using Conductor (also called copper or load) Losses only will approximate the R of larger (>500KVA) transformers.

One formula I've seen is W=[(Conductor losses in KW)F^2]/(Rated KVA) x F. Where F = Load Factor (Fraction of Rated KVA used). Then use Ohm's Law to solve for R.

RE: Determining Transformer Resistance & Reactance

a

RE: Determining Transformer Resistance & Reactance

It seems like a) can be shown to be correct.

assume the losses occur at rated (base) current.
R=[I^2*R]/Ib^2=[Ib^2*R]/(Sb^2/Vb^2)

Zb=Vb^2/Sb

Rpu=R/Zb =[I^2*R]/[(Sb^2/Vb^2)*(Vb^2/Sb)
Rpu = [I^2*R]/Sb

RE: Determining Transformer Resistance & Reactance

    In my oppinion, confusion arise from "load loses" definition. If it sould correspond to short circuit loses (at rated current) also called "copper losses", then a) is right. Otherwise if it sould correspond to total load losses at rated voltage and current then b) should be:
 %R = 100x(Total load loses - no-load losses)/rated power
    I think a) is the correct option. When internal impedances are given in per unit or per cent, bases values must correspond to rated values. Then:
    Zb = (Ub^2) / Sb = Sb / (Ib^2)  Or  Sb = Zb*Ib^2 = rated power

    puR = R / Zb = (R*Ib^2) / (Zb*Ib^2) = (copper losses) / (rated power)

    That all is only applicable to one phase transformers. For three phase trasformers that shall be applicable to their "equivalent one phase transformer". The easier way to do that is:

    1.- Take as Base Voltage the rated voltage (line to line voltage) divided by square root of 3
    2.- Take as Base Power the rated power divided by 3
    3.- No modification for Base Current or Impedance.
    4.- Consider as copper loses its third only

    Hope to help you

Julian

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources