DC Bus bar clearance

DC Bus bar clearance

DC Bus bar clearance

(OP)
We are conducting a retrofit on our DC switchgear (750V railway) and additional bus bars will be installed. However, due to space restrictions we have an issue on the allowable clearances between the positive or negative bus bar and the enclosure or any metallic support. Please enlighten me on the allowable clearances.
TIA

RE: DC Bus bar clearance

It depends on where you are and what codes apply. UL 891 would require 1 inch.

RE: DC Bus bar clearance

And you can always pack some suitable insulating sheet between the bus bars where they are fairly close. This is often a good idea anyway, because it prevents things falling directly across the bus bars, while still allowing adequate cooling.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources