11kV air gaps

11kV air gaps

11kV air gaps

(OP)
Hello,  Is there a standard distance for air gaps between pahses in 11kV cable boxes?  Thanks

RE: 11kV air gaps

Probably, and it probably depends on where you are and what codes and standards are applicable.

RE: 11kV air gaps

it depend of used cable type, but 130 mm ( 5 inch) is enough for bare cond.

RE: 11kV air gaps

It depends on the type of termination too. For dry boxes, the manufacturer designs the cable box to suit the lightning impulse withstand voltage and will specify whether the box is suitable for fully insulated terminations or partially insulated terminations. Fully insulated could be elbows, or cable terminations with boots over the lugs, partially insulated terminations only have insulation on the cores. Compound boxes have much less clearance, typically 45mm ph-ph and 32mm ph-gnd for 12kV.
Regards
Marmite

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources