(OP)
Can someone help to clarify the "Primary Drainage System" as described for roof ponding requirements?  

I have a roof with 1/4" per foot slope to the interior of a building, where roof drains are located (The interior is 1'-3" lower than the permeter).

My question is that if we provide a secondary, or overflow scupper, and this is elevated like 2" above the primary drain, can this drain be tied into the main drain stack below the roof?  If so, can I only design the roof for 2" of water, vs almost 1'-3".  Or do we need to provide a completely separate drain system (ie 2-full runs of pipe) to be able to do this?

RE: Roof Ponding

The overflow needs to be fool proof, i.e. if your drain stack blocks up then it still needs to work.

RE: Roof Ponding

(OP)
Thanks.   I went to the ICC and their code chat had a post citing a code reference that the secondary drain needed a separate point of outlet.  

RE: Roof Ponding

"IPC 1107.2 Separate systems required. Secondary roof drain systems shall have the end point of discharge separate from the primary system. Discharge shall be above grade, in a location that would normally be observed by the building occupants or maintenance personnel."

Don Phillips
http://worthingtonengineering.com

RE: Roof Ponding

We have our overflow drains thru the wall like a scupper so that any flow would be noticed!

RE: Roof Ponding

If your secondary is 2" above the primary, you may have to design for more than 2" anyway.  You have to account for the hydraulic head as well as the static.  You'll find this in the rain loads section of the IBC or in the same section of a state code based on the IBC(e.g. 1611 in the FBC).  You can get hydraulic head information from the ASCE 7 and the design rain event from the plumbing code (chapter 11 I think).

RE: Roof Ponding

And remember--what this thread is discussing is "blocked drain design," not "ponding."  If a roof slopes more than 1/4" per foot, ponding is not an issue, because the member will typically not deflect enough to keep water from draining towards the drains.

If a roof slopes less than 1/4" per foot, ponding should be checked, even if the drains can never get blocked up.

DaveAtkins

RE: Roof Ponding

Quote:

If a roof slopes more than 1/4" per foot, ponding is not an issue

Dave, not sure about that.  In most cases it is true (and in fact AISC K2 mentions "flat roofs") but in some cases you can have 1/4" foot slope into discrete and closed-off valleys which have only one primary drain....say with a 4" ridge height, with scuppers way off in the distance.

The primary plugs up and this bath tub fills to the brim.

You'd design for the weight of the water, yes, but even with the 1/4"/ft slope I'd be very concerned about ponding in the discrete valley areas since the water there would flow to the lower areas first, pond there, and if your framing system wasn't stable per AISC K2, then you could possibly have a real issue with second-order load application of the water.

RE: Roof Ponding

JAE

In the situation you describe, there needs to be a secondary roof drain there. I often try to make sure that the architect and the plumbing designer follow thru on their design properly so that it does not come back on the structural guy.

RE: Roof Ponding

The secondary drain is the scuppers beyond.  They design for the extra weight of the water in the "tub" and then assume that any excess water goes over the ridges and finds its way to the scuppers.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources