PLC input ripples

PLC input ripples

PLC input ripples

(OP)
Dear All,

I would be grateful if someone helped me with this. I am planning to use ABB AC31 PLC. one of the inputs to the PLC will be the output of a single phase full wave rectifier uncontrolled bridge. when using smoothing reservoir capacitor, still the voltage will have some ripples.Are these ripples harmful to the plc? or i shouldn't care that much about them?

If I should totally gt rid of the ripples, how can i do that?

(by the way, the bridge output is inserted to analog input point of the plc)

RE: PLC input ripples

The ripple will not be a problem if you are talking a Digital IN.  If you are talking an Analog IN it may be a problem.

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

RE: PLC input ripples

Connect the plc input to the bridge output via a resistor of a couple of kΩ or so. Put a relatively small capacitor directly across the PLC input. The small cap will smooth out the ripple and the resistor will decouple it from the main supply. It won't be a perfect representation of the DC level + ripple, but your PLC isn't fast enough to care.
 

----------------------------------
  
If we learn from our mistakes I'm getting a great education!

RE: PLC input ripples

I know on ab contrologix their is signal conditioning on inputs to look not look unless the signal changes over a predetermined time as configured on card.  Siemens though has diagnostic ripple on its input cards, this might be a problem if using these type.  This can be disabled  Not sure on ABB plc.  I would think they would have some scheme similar to above manufacturers, since they always seem to copy off of each other.

RE: PLC input ripples

(OP)
Thank you guys

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources