Explain ASD vs LRFD to a dumb ME
Can someone explain in really simple terms the difference between ASD and LRFD? ASD seems easier but is it going away?
I was reading through the new AISC Steel Construction Manual about the two methodologies and, aside from the different load combinations, was having a hard time seeing a clear distinction between the two.
RE: Explain ASD vs LRFD to a dumb ME
ASD has changed from Allowable Stress Design to Allowable Strength Design. There used to be different equations for ASD and LRFD (they were completely different specs), but now there is one equation for design strengths that are divided by a safety factor, omega, for ASD and multiplied by a strength reduction factor, phi, for LRFD.
The only real difference now is that ASD provides a constant factor of safety for all designs regardless of load types while LRFD provides a higher factor of safety on the loads that are less well defined (1.6 LL factor compared to a 1.2 DL factor). At a LL/DL ratio < 3, ASD is more conservative, at a LL/DL ration = 3, it is a wash, and at a LL/DL ratio > 3 LRFD is more conservative.
Any additional questions, please ask.
OK - my stupid analogy:
You have a small stream and need a log to drop over the stream so your ballet cow can dance across it. The log needs to be strong enough not to break under the weight of your cow and it needs to be stiff enough so the log won't sag too much under her weight.
Cow weighs 500 lbs. Log spans 15 feet.
ASD
You know that the wood of your log can be stressed to 1000 psi before it breaks. So you need to find a log large enough so that the wood is not stressed to 1000 psi. In fact, you want to limit the stress with some safety factor to make sure that you are OK.
So you find a log large enough such that the stress is limited to only 600 psi. (i.e. your maximum allowable stress is 0.6 x 1000 = 600 psi.)
So you have a safety factor against failure of 1/0.6 = 1.67.
The equation looks like this:
fb = Stress from weight of cow
R = Strength of log
0.6 = safety factor
0.6 x R > fb
LRFD
You still know that the log can be stressed to 1000 psi before it breaks. You also know that the weight of the cow used to find the stress in the log might be plus or minus a few pounds. So because of this uncertainty you apply a safety factor to the weight of the cow -say 1.6. Also, you know that the 1000 psi limit varies a bit with different logs so you apply a little safety factor to it - say reduce the 1000 psi to 900 psi just to be safe. (i.e. 0.9 factor)
So you find a log big enough so that it will theoretically break when a 1600 lb cow is placed on it and you only count on 90% of its strength.
So the equation looks like this:
R = Strength of log
0.9 = resistance factor
1.6 = load factor
0.9 x R > 1.6 x fb
What LRFD gives you that ASD doesn't is the ability to use different load factors (the 1.6) depending on the variability of the load. Dead loads you usually know pretty well. Live loads vary all over the place.
Also, the resistance factor can be varied depending on the variability of the strength estimates that exist with different materials and different failure modes. Abrupt, highly variable failures need lower resistance factors
while flexible, ductile failure modes can have higher factors.
I've used stress in my LRFD example, but most LRFD specifications use moment, shear, or force variables instead of stress.
LRFD allows proper, balanced statistical probabilities of failure while ASD has a single safety factor independent of how well you know your cow.
In ASD you treat dead and live loads equally. For example, if you have a case where your dead to live load is 1 to 1 (say 200 kips dead and 200 kips live) the safety factor would be exactly the same as if your dead to live ratio was 1 to 3 (say 100 kips dead and 300 kips live) given the same total load.
LRFD recognizes the inherent unpredictability of loads and assigns a much higher "factor of safety" to live loads (we increase them by 1.6), whereas it recognizes that dead loads are most likely much closer to what you calculate (we only multiply dead loads by 1.2).
By the same token, LRFD also recognizes the uncertainty of different failure modes. For example, flexural capacity of a concrete beam is fairly predictable; therefore we count on 90% of the theoretical value. Shear in concrete, on the other hand is much less predictable; therefore, we only count on 70% of the value. I believe ASD also recognizes this to some extent, by applying different factors of safety to different failure modes, but I only really worked ASD for a few months, so I don't remember.
When all is said and done, you design so that the decreased member capacity with which you rely exceeds the capacity required by the factored loads.
In ASD you take the total loads that you expect on the structure and apply a single factor of safety to the members (say 2) regardless of the nature of the load.
It's worth mentioning that in the steel code (AISC), the publication of the 13th edition of the code attempts to unify the two. The way they did this was to calibrate load factors and resistance factors so that ASD and LRFD would yield the same factor of safety at a certain dead to live load ratio (don't quote me on this, but I believe it's 1 to 2).
My apologies for the length of this post.
A shear failure on the other hand is brittle. Unless you actually see the beam and see some shear cracks forming, you really wouldn't be able to see anything going on in your structure before it fails (assuming it was over loaded). As a result, you go the extra mile to avoid these failures and you do so by reducing their theoretical capacity by a higher amount than you do for ductile modes of failure.
Dik
They "cram" LRFD down your throat because all the major codes are moving this way. As dik mentioned, it provides a more uniform (and consequently reliable) factor of safety.
As for more conservative, that entirely depends on the dead to live ratio. As I mentioned in my previous post, ASD and LRFD were calibrated at a specific dead to live ratio (I believe 1 to 2). At this ratio the true factor of safety is the same. If your dead to live ratio is lower than 1 to 2 (that is, more dead load) then yes, ASD is more conservative. However, at anything above this ratio, LRFD is more conservative (as it places more uncertainty on live load).
I'm not knocking ASD- I know it's been used for many years quite successfully. But LRFD is not entirely without merit.
I like to think of it as large L/D --> use ASD because it's more economical. Then again, I'm a metal bldg systems guy at heart, LOL.
I take it that the .9 resistance factor allows for the milked cow condition?
Mike McCann
McCann Engineering
Not almost anymore!
It depends on the type of material and the type of force and is lower for materials and the type of forces that have a greater 'scatter' of test results. It's to make up for uncertainties of how things 'behave'.
In 1965, we were the first engineering class at the U of Manitoba to deal exclusively with 'Limit States' design, the precursor to LRFD and consequentially 'Working Stress' design (ASD) was only touched on for historic reasons. So, it's been around for a while (40 years).
Dik
Varation in:
Depth of log
Width of log
Strength of the wood
Whether there were termites in the log
The span length
The accuracy of the equations that tell us what the log will support.
The 1.6 load factor accounts for variations in:
The cows weight - I guess it depends on milked/not-milked and pregnant/not-pregnant but let's not forget the steroid question.
I believe it actually stands for "resistance factor" as in Load and Resistance Factor Design.
The term "material property" factor is a bit misleading because it not only responds to variability in material properties but also geometric property variations (i.e. variability in depth, width, location of rebar, diameter of bars, thickness of flanges).
Mike McCann
McCann Engineering
Not almost anymore!
1.) The ASD Manual (the Green Book) has not been updated since 1989. The specificatyion part of it has not been updated since the 70s. All current research has been conducted using limit stares design.
2.) In ASD, the factor of safety is based on probability for (3) itesm.(A), the probaibility of errors in erection, (B) the probability of errors in manufacturing, and (C) the probability of errors in the "simplified" mathmatical equations we use. By the time the building is in service, these probablilities are have been accounted for and there is really no factor of safety any more.
3.) If you really read the Seismic manual, you have to use LRFD anyway.
4.) In reality, as stated above, ASD does not exist anymore. It is now strength design, which in essence is LRFD, just with the factors moved aroud to make the old method seem like it is still there.
Pretty soon we will be having the same conversation about concrete and the ACI's method of using compatibility instead of balanced steel. Those of you using 1.6 and 1.2 in Concrete and not performing a compatibility analysis to determine tesion / compression control are not doing your calculations correctly.
Have fun!
Dik
Your statement number 2 implies that ASD is not as safe as LRFD, which is not true in simplistic terms. In fact, much of the statistical analysis done by Galambos and Bruce Ellingwood many times calibrates the load-factor/phi-factor level of safety to that of the traditional ASD safety factors.
With very high live load to dead load ratios, LRFD will result in heavier members than ASD and with low ratios the resulting designs are heavier with ASD.
ASD exists in the latest AISC manual and uses one Ω factor, replicating what the 9th edition of the AISC ASD manual used, but also incorporating the latest research.
ASD simply doesn't reflect at all the variations in loads and resistance factors and so provides a variable probability of failure while LRFD's probability of failure is much more constant with different loading conditions and with different materials.
I use LRFD all the time now (grew up on ASD).
The old ASD (allowable stress design) is the same as the new ASD (allowable strength design). The difference is it now has you check the strength (P, M, etc) as opposed to a stress (fb, fc, etc). That is the only difference to the approach, which really isn't a difference at all. The equations have changed because there has been much research since the last ASD specification.
I've studied all of the supposed benefits of LRFD over ASD, and I don't see it. For my money, I'm using ASD all day long. The frustrating part of LRFD is you still have to run the service load combinations to check serviceability of the structure. Why do two analyses when one will check both strength and serviceability? Maybe you can lighten up your members a little for certain cases with LRFD, but I don't design that close anyway, so where's the benefit?
I personally don't see the big deal in using LRFD, so might as well go that direction and get used to it. Just my $0.02
You're absolutely right. The reason they included a combined specification was to try to coax everyone into LRFD. My steel professor even seemed a bit disappointed that they included ASD at all in the Specification.
Your professor might do some work for AISC. The inclusion of ASD and LRFD wouldn't make the Manual 2x as hard to create, but would definitely add a lot of time and effort. Remember that volunteers, for the most part, put that thing together.
I personally do not like having ASD in there simply because it muddies the water. Take a look at the hanger prying action stuff, for example. It's also VERY easy to mis-read a table and yank an ASD number when using LRFD.
He's a task committee member.
You have a 4x12x0.25m concrete shear wall that resists a wind load applied on a 30x12 m sq. tributary area. You were told to design for a 75km/h wind speed, which applies about 0.35kPa pressure. For this wall you needed a tie down that is capable of resisting 48kN tension. You decided to apply a factor of safety of 2.0, therefore, your tie down is capable of resisting 96kN tension. Well, the building was hit by 85km/h wind (13% increase in speed), which applied 0.44 kPa pressure. The tension in your tie down is 96kN. It yielded. What happened to you safety factor of 2.0?
I disagree. The reason they went to LRFD back in 1986 or so, and the reason they only issued LRFD specifications with the silver and dark blue manuals, was to coax designers to use LRFD. Designers balked and wanted an ASD specification that reflected the latest research. The combined specification is to please the portions of the steel community that wanted a comparable ASD specification. In my mind, this is AISC saying "we give up, here's your ASD back."
271828:
The researchers want it, it's inevitable, so we may as well get used to it? What about the designers that use these specifications? Is their input worthless? I don't mean to belittle the researchers and the academics, but as designers, we should make our voice heard as well.
As I mentioned above, I don't get the factor of safety argument. We don't have structures failing all over the place. Why is there a push to change a system that's working fine, especially when the change is to make it more complicated for no good reason?
With computers, we can put in 100 load combinations as quickly as we can put in 50, so why not? How about keeping things simple? Does anybody do hand calculations anymore? Run one check ASD, determine strength and serviceability with the same loads, or have to do it twice with LRFD? How is this beneficial to anybody?
The 13th edition is a limit state design in either ASD or LRFD. They combined ASD and LRFD to showcase how "similar" the two could be and as a result ease the transition to LRFD for those designers who had been using ASD for many years.
AISC did capitulate a bit in a sense, since they really would rather not have included ASD, but they did so looking to eventually phase out ASD. The 13th edition can be considered a "transition" specification. It's the "rosetta stone" for ASD designers.
I guarantee you AISC is most definitely not "giving up".
As a former designer, I sure hope their input is not worthless or ignored. A very sizeable portion of today's engineers learned LRFD first and won't give a rip if ASD goes away. It won't be long at all until the vast majority of designers will have learned on LRFD. Calculating and using wu to get Mu and then using w to get deflections is old hat to them.
I'm a researcher nowadays and there seems to be an inevitable march away from deterministic approaches toward reliability-based approaches. I personally HATE this because I despise probability and reliability as subject, but it seems completely inevitable at this point. Like it or not, researchers have fairly strong voices when it comes to Spec. writing, so these approaches will have a strong influence.
How is this stuff beneficial? To be honest, I cannot answer that for most situations. I think some of the worst technical authors have written most of the papers on this subject. I read papers and do research every day and my eyes glaze over when I read most of these.
For some types of checks, going probabilistic makes great sense. Take floor vibrations for example. The loading is almost totally random. Any criterion that claims "OK" or "NG" is hard to justify (other than not having anything else). Some of the newer methods will eventually lead to the ability to tell an owner that he has 2%, or whatever, probability of complaints.
I got my BS in 2001. I learned LRFD in school, but as a designer, I use almost strictly ASD. This is common for many of my peers that went through school about the same time, who never once studied ASD in school.
frv:
Sure, the unified specification is based on limit state design, just as the old ASD was. Further, the unification of the specification shows how the equations are the same for a given limit check. The changes between the 9th edition ASD and the 13th edition ASD are due to research that has taken place, not a change in the philosophy of any of the checks.
This argument can go on ad infinitum.
The equations are the same, but the the safety factor is not.
I did work for one firm, however, in which 89 ASD was used. The younger guys there hated it and saw the firm as backward for not letting them use what they learned in school.
I do not claim to know which is more typical, my experience or your experience. As time goes on, however, I have to think more and more folks will come out of school thinking LRFD = Steel Design, so won't give a rip about ASD.
ASD actual stress are computed for actual loads and held below a maximum allowable stress.
Which method gives you more control over your deign?
(Hint: With ASD you know stresses at every point in your cross section and can compute actual deflections)
Cripes, the only difference is in the fact that LRFD weighs the safety factors on each load and the member strength to give you a much more rational level of safety.
I grew up on ASD - don't have anything against it. It is fine, easy, straightforward, etc. But it s*cks when it comes to measuring safety consistently.
DRC1, ASD's stress is "held below a maximum allowable stress" as you say. The problem with it is that the amount you hold it down is totally arbitrary - a historic one-shot safety factor that has no rationale behind it.
You say you know the stress at every point for "actual loads", but those "actual" loads are still just estimates of variable loads. Your actual stress depends on a live load that has been measured in the field as having incredibly high variability....so it's not anymore actual than the factored loads of LRFD.
I've learned both methods. Both are fine.
Yes you can argue that the extra value in knowing you have a more rational, consistent safety factor in LRFD is of questionable value in most structures. I won't argue that.
It's just that I can't believe how many engineers I've heard bashing LRFD simply because of a few extra steps - and then try to insinuate that there is some lack of rationale or intelligence in LRFD.
I've converted to LRFD (after using ASD more than 15 years) and it's not that big of a deal to use nor that cumbersome once you start using it.
Both methods have been set up to give similar results and both methods are "good engineering practice." But I can't agree with the implication that ASD is somehow superior or offers more control to LRFD.
Uniform safety and a reliability based rational design is LRFD.
Used both ASD, the not so adopted LFD, and now LRFD and I don't see the big deal.
Same issue we had with metric, you're an engineer for cripes sake, shouldn't matter what units you use.
![[pipe] pipe](https://www.tipmaster.com/images/pipe.gif)
Qshake
Eng-Tips Forums:Real Solutions for Real Problems Really Quick.
Also, the reliabiltiy of a design system depends on how it is used. With multiple load cases to consider, LRFD demands computer based designs. You've heard it yourself. At the end of any LRFD seminar, attendees with glaxed eyes start asking for the software that can perform all these calculations. Well, for my money, as soon as the designs are done by engineers who cannot design the element by hand, reliability goes down.
LRFD factors are indeed adjusted as you say.
What is done is that statistical analyses are performed to determine the weighted variabilities of different load cases. (i.e. live load is more variable and thus has a higher load factor).
Then, a measure of probability of failure is determined based upon historical design methods like ASD.
This probability is a β factor that is based upon the combination of load factors / phi factors. Then the LF/Phi factor is adjusted down or up to reflect the overall probability of failure desired.
The statistics are still there (i.e. the load factors are of different values based on variability of loads and the phi factors are relatively different depending on the material and the mode of failure).
They haven't abandoned the reliability theory at all. That is incorrect.
Correct me if I'm wrong, but I thought the LF/Phi factor was also adjusted down or up to more closely match designs done using ASD.
The resisant virtues of the structure that we seek depend on their form; it is through their form that they are stable, not because of an awkward accumulation of material. There is nothing more noble and elegant from an intellectual viewpoint than this: to resist through form. Eladio Dieste
Never, but never question engineer's judgement
I think that's the wrong way to look at it.
I'm sure an engineer or builder 8-9 decades ago would ask the same thing when faced with newfangled materials, design methods, and construction methods. Would we be better off today if no advances were made since the 1920s? 1960s? Do we think structural engineering knowledge advanced to a practical maximum level for all time in the 1980s (a pretty arrogant claim if you ask me)? I don't claim to know what structural engineers will be able to do with advances made between now and, say 2050. It's not about "solving a problem" in most cases. It's about "moving forward with new and better information." Is Beam 437 in a given building directly influenced? Probably not, in most cases. That's not the point.
But a benefit of LRFD often cited is increased reliability. In that regard, I'm not so sure I agree. As I said earlier, the multiple load cases inherent in LRFD demands more use of computer aided designs.* I believe that, as more designs are carried out by computer, engineers will lose the feel for what constitutes a safe design. In that regard, I believe that overall reliability suffers. Is advancing the state of the art worth a decrease in reliability?
*Note: While it's true that IBC and ASCE7 require multiple load cases for ASD design, ASD traditionally used one or two load cases, and no load factors. Including load factors in ASD, as IBC has done in Article 2.4, essentially converts ASD into a Load Factor Design.
If you take a design - say a steel beam spanning 30 feet, and design it with ASD for a set load. Then take that load and design it with LRFD assuming it is all dead load. Then design it again with LRFD assuming it is all live load.
Here's an example:
Per AISC 13th Edition
Span: 30 feet
Load: 3 kips/ft (service)
Unbraced length: 0 ft
Fy = 50 ksi
ASD
Moment = wL^2/8 = 3(30)^2/8 = 337.5 ft-kips
Ωb = 1.67
Mn = Mp = FyZx
Zx (required) = 337.5(12)1.67/50 = 135.3 in^3
W21 x 62 (Zx = 144)
LRFD with all dead load
Mu = 1.4(337.5) = 472.5 ft-kips
φ = 0.9
Zx(required) = 472.5(12)/.9/50 = 126 in^3 (which is less than the ASD requirement)
W21x55 (Zx = 126)
LRFD with all live load
Mu = 1.6(337.5) = 540 ft-kips
φ = 0.9
Zx(required) = 540(12)/.9/50 = 144 in^3 (which is more than the ASD requirement)
W21x62 (Zx = 144)
So LRFD sort of brackets ASD depending on the DL vs. LL ratio.
I am totally with you on this one, as I've typed around here many times. There *will* be another major collapse at some point due to mis-use of a black box.
I doubt that LRFD is to blame, however. The advent of the cheap personal computer and the currently popular, un-named automated steel design system, combined with tight structural fees combine to cause the danger, IMO.
Structural fees and schedules are so tight that it is very tempting to press "Run" then "Export to dxf" (or worse yet, "Export to SDS/2") and then never look at it again. I'm sure most of us can point to a pet case or two of that. I have one in mind that actually caused failure.
I'm going out on a limb to come up with an example of possible future analyses that might be carried out with LRFD, but not ASD. Here goes. Imagine that I have a load that is genuinely better represented by a probability distribution than a deterministic design load. If I have separate load and resistance factors, then this can be dealt with. If one factor of safety exists for both sides, there's no way to approach the problem. I can think of several good examples: earthquake, wind, footfall forces, etc.
With all due respect, DRC1, ASD was the method one of my mentors used from the 1930's. He started his career in 1927 and was very comfortable with ASD. Fine and dandy. OK with me.
LRFD isn't a quantum leap...no one ever said it was. It's just based upon statistical balancing of variabilities. I did my thesis on Phi factors for metal deck slabs and read multitudes of papers on how LRFD is developed. Yes, it balances with ASD for general loading but does allow you to consider the variability of loading AND of the material variations.
From that research, you would know that your reference to the "variability of the strength of structural steel" has very little to do with the safety factors. 0.6Fy isn't about whether your Fy equals 36 ksi or 38 ksi. The 0.6 factor is simply, historically, a feel good level of safety for design. It's not about variability of steel strength - that only accounts for about 3 to 5% of the total variability of our level of safety.
LRFD does NOT assume "uniform plastification" of a member...it is based upon a limit state within the elastic range (i.e. at yield, not beyond it).
I agree with you that LRFD doesn't give you any magic information better than ASD other than accounting for variability (thus my design example above).
Here's how I understand the sequence. LRFD theory started out with a set of assumptions and goals. Correct me if I'm wrong, but I believe one of those goals was to provide the same reliability as ASD. After all, we didn't have a reliability problem. If I understood the seminars, the initial result turned out to be more economical than ASD. Then, LRFD's β factor was "adjusted" to bracket ASD, or bring it more in line with traditional designs. So, instead of a design approach that had the same reliability as ASD and better overall economy, LRFD was adjusted to provide the same overall economy and better reliability. It's at that point that one of the initial goals (same reliability) was abandoned.
I am with others in that the codes are getting into overkill mode with the attempt to get more and more precise with design methods - chapter 10 of the ACI code comes to mind - but my only main points in this discussion are:
1. LRFD isn't that hard to use (as some have suggested)
2. LRFD provides a better rationale for safety factors and produces a better level of reliability than ASD.
3. ASD is fine to use...just has a variable level of reliability that may or may not matter.
Having ASD and LRFD in the same steel manual is fine, I guess...but when I first saw it my mind immediately thought of a scenario where some confused, inexperienced engineer would wrongly use different tables for a single design and screw up.....like using a non-factored dancing cow load on an LRFD log.
The reduction in E is something entirely different. This is done when you check stability of frames under Appendix 7 of the 13th Edition of AISC.
Yes. That would be the case regardless of what program you're using.
Check out this previous thread - Per Chapter C of the new 13th Edition AISC Spec, the Direct Design Method uses a reduced EI and EA for the analysis for the purpose of accentuating the Pdelta effects a bit:
thread507-201140: Approach for designing unbraced (steel) frames.
A lot of threads have broached this subject, but to summarize direct analysis:
1) Use computer software that has p-capital delta and p-lower case delta capabilities (i.e. rigorous second-order capabilities)
2) Reduce the stiffness of all members that contribute to lateral stability (EA and EI)
3) Apply notional loads OR model the frame with an initial out-of-plumbness.
4)Analyze and select compression members with k=1
It's just a matter of time before we get a corporate sponsor.. "Arby's Modulus"
the reduced E is to account for residual stresses in the fabrication process. Given these stresses, some parts of the cross-section will yield prematurely. This essentially excludes those parts of the cross section from contributing stiffness to the stability of the structure.
Be on the lookout for an upcoming AISC Stability DG. It is very large and has dozens, if not hundreds of pages of full bldg examples--actually borders on overkill IMO. It was in the review process at least a year ago and I'm surprised it's not out yet.