grounding substation Bollards

grounding substation Bollards

grounding substation Bollards

(OP)
Does anyone know if bollards in a eletric utility substation must be grounded.  The Bollards are 4 inch diameter steel pipes filled with concrete, which are used as a protective barriers for equipment.  There is an extensive ground grid in the sub to which the bollards are not currently connected.  I'm reviewing IEEE-80 for clarification.  Any ideas?

RE: grounding substation Bollards

I would say they need to be bonded to the ground grid, just like any other piece of steel structure.  

RE: grounding substation Bollards

I wouldn't bother.  They are not likely to get energized and still be in a position that someone could touch them without touching whatever is energizing them.

RE: grounding substation Bollards

During a fault, there could be a potential difference between the earth where the bollard is installed and the grounded equipment that could be nearby.  



RE: grounding substation Bollards

I would consider then equivalent to metal fence posts. Ground them. I was on a 25MVA sub last summer. The plans called for bollards and called for them to be grounded. I can not think of a piece of metal inside the substation fence that was not grounded.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: grounding substation Bollards

I ground the bollards on all my MV equipment including bollards for oil filled padmount transformers, MV switchgear, etc. at industrial sites.   

If this is a true electric utility substation everything inside the fence including the fence is grounded at least for the specifications of the two utilities for which I have done work.

RE: grounding substation Bollards

Not only ground, but visibly grounded.  Upon first entering the substation one is to check to make sure that all grounds are present and accounted for; missing grounds to be reported immediately.  Crews wouldn't work around an ungrounded bollard.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources