Shear strength acc. ACI 318R-02
the shear strength provided by concret Vc is given in clause 11.3.1.1. The version which I have says:
Vc=2*(sqrt(fc')/6*bw*d
in the internet I found:
Vc=sqrt(fc')/6*bw*d, but realted to the same code release.
Same appwears for the limit of Vs (clause 11.5.6.9):
Vs=8*sqrt(fc')*bw*d
and
Vs=2/3*sqrt(fc')*bw*d
WHAT IS CORRECT ?
Thank you very much,
Martin
RE: Shear strength acc. ACI 318R-02
Upgrade to the latest edition and go metric. ACI 318M-05.
I'm not sure where you get the /6 in the Vc formula.
ACI 11.3.1.1, Equation 11-3 shows:
      Vc = 2(√f'c)bwd
The value in section 11.5.6.9:
      Vs = 8(√f'c)bwd
is a maximum limit on your steel shear reinforcing contribution.
I don't see where there is a Vs = 2/3(√f'c)bwd
Vc and Vs are two different things.
bender35,
When you use a new formula that you are no sure about, check it to make sure it makes sense. In your case a higher area would have resulted in a lower shear capacity - obviously something was wrong.
It doesnt work so well on this formula, but usually putting the units into the formula should give you the correct units as a result (i.e kips/lbs for a force or psi for a stress).
Check in ACI 318-05 (SI units), you will find:
      Vc = 0.17(?f'c)bwd
11.5.7.9:
      Vs = 0.66(?f'c)bwd
the first you mention for Vc and Vs are in imperial  units, the second are in  Metric units