depth of flow in pipes

depth of flow in pipes

(OP)
hi can anyone help me I have to design a foul drainage network for a housing estate. Dont have a software program so its the old fashioned way! Have most details worked out but the proportional depth of flow is what I have difficulty with. If anyone has an example of a pipe design I would be grateful!!Thanks

RE: depth of flow in pipes

2
What exactly are you trying to do?  Generally, proportional depth of flow wouldn't be an issue in design, that is you are either designing at full or half-full (for which the velocity is the same in both cases, hence the equation's simple).  If you truly need depth of flow for any other flow, I usually use the nomograph for partial flow in circular pipes (assuming of course you have circular pipes).  This tool can be found in several places including the CE reference manual by Lindbergh and the Concrete Pipe design manual by ACPA.  There's also someone who posted a spreadsheet recently under the spreadsheets forum that supposedly will get you close.  I haven't tried it yet.  In summary, there's no simple formula for what you've asked about, but it's generally not necessary for standard designs.  Let me know if you need the nomograph, I could probably find one as a pdf.

RE: depth of flow in pipes

unless your prefer to do it all by hand, there are free software programs out there to help with the design.  EPA SWMM is a full featured program that could design your project and can be easily downloaded from the internet.

RE: depth of flow in pipes

(OP)
Thanks for that but does that program only deal with stormwater design, as I require a design package for foul waste network

RE: depth of flow in pipes

generally waste is considered to have the same hydraulic characteristics as water.

RE: depth of flow in pipes

Typically here everyone runs a minimum of 6-inch for house laterals or 8-inch sewers for residential developments up to a point (i.e. collector sewers).    

You can back calculate the needed sewer size using EPA's rule of 400 gpd / home X peak factor (see 10 states standard).  Then use Mannings Equation solve for A using V = 2fps.  You probably dont want the sewer to run more than 1/2 full worst case scenario.


10 States Peak Factor
Peak Factor = (18 + SQRT (P))/(4 + SQRT (P))
P = Population in Thousands

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources