Concrete Tank - Concrete Lid poured on site and craned onto tank
I have a little spin to add to a standard concrete tank design. With the underground concrete tank I am working on, the contractor/timeline requires to form and pour the lid on the ground while working on the floor and walls. When the walls are complete with adequate cure time, the lid(s) would be craned on to the tank.
Can anyone recommend information on specifying lift loops and guidance on spacing and associated reinforcing details required for the lift?
The lid(s) also have openings of various sizes and arrangements to allow future mechanical replacement, ie pumps, etc.
Thanks.
Thanks.
RE: Concrete Tank - Concrete Lid poured on site and craned onto tank
Stevemort: How much training does the RISA program require and approximate cost for program/training?
herewegothen: That would be great if you can send the details on lifting sockets.
What is FEA?
Here is secondary problem associated with adding top on after walls are poured, what would be the best way to connect the lid to the walls to give walls stability to resist deflection from backfill loads?
I have designed some tanks recently (about 40 m dia & 3 m deep with up to 4 m of soil over the roof & 3 m into the ground water). These have been for wastewater pump station emergency overflow situations. I design the roof using precast beams on top of columns & hollow planks (conc slabs with longitudinal holes) on top. I check the design three times - for transfer (they are pretensioned), loading from a concrete topping (eventually will become a composite slab), then loading from the soil after composite action can be established.
This method is used so that no roof formwork is required (that would have to be extracted out of the tank later) & the only opening is the final access hole.
The principle of 'lost formwork' has proved to be quick & economical for the very high loads from the soil loading. Tank floor is constructed, walls & columns next, then all the rest of the construction will be from above the tank (outside the tank wall perimeter).
I can't see that this method would be economical for a lightly loaded roof.
You might want to think about adding some extra reinforcement for impact loading.
What would be the best way to connect the lid (either cast on the ground and craned on top or pre-stressed craned on top) to the walls to give walls stability to resist deflection from backfill loads?
I was thinking of dowelling and epoxy into the top of the walls thru holes in the lid and epoxy to seal - what do you think?
Regarding contraction joints; 60 feet is maximum length of wall recommended without joints with 30 to 50 feet being more common, would you consider that length measured along each wall or measured along the tank length?
For example: sanitary tank 60 feet long x 15 feet wide with 4 compartments of various sizes.
Do you add the perimeter dimensions to determine the need for joints in this case 150' or just go by the tank length of 60' and that would not require any joints?