Hi All,

I am designing a 5kV distribution system in underground ductbank, utilizing single-conductor, shielded phase conductors with an equipment grounding conductor included with each parallel set.  System is low resistance grounded.

Are the equipment grounding conductors required to be the same spec as the phase conductors?  Or, could it just be a green insulated 600V cable?

Thanks in advance for your thoughts.

Regards,

EETD

RE: Ductbank EGC's

No the EGC's aren't required to be the same spec (i.e. MV cable) as the phase conductors.  It doesn't even have to be green after it is above a certain size.  I usually use black THHN or XHHW for my EGC in MV systems.  It is easily distinguishable from the MV conductors.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources