Earthing of Mobile Equipment

Earthing of Mobile Equipment

Earthing of Mobile Equipment

(OP)
Hi All,

I am doing the preliminary design for a mobile mining unit and trying to work out what to do with the earthing. The unit is running on tank tracks and moves about 30m every 3-4 days. Onboard there is a trailing cable running from an external cable reeler to a 6.6kV RMU (which also feeds another mobile unit that follows it) and then a transformer which supplies the onboard MCC with a running load of about 800kW (DOL and VSD driven motors and auxiliaries).

I am looking for advice from anyone else that may have undertaken something similar to ensure that the earthing, touch and step potentials for the unit are adequate. Any advice would be gratefully received.

Thanks

Goldyvb

RE: Earthing of Mobile Equipment

Dear Gold,
In the USA, mining is governed by the government agence MSHA which requires that the power for portable or mobile equipment be resitance grounded with a 25 amp grounding resitor. Common voltages for the utilzation equipment are 4160 and 7200 volts since the loads are large such as draglines and electric power shovels. There is also a requirement that the grounding conductor be continuously monitored.(Ground check relay usually with a pilot wire in the trailing cable). Look in the IEEE green book for more information as well as other references.
Jim
 

RE: Earthing of Mobile Equipment

Hello Goldyvb,

Jim (lansford) is right about the United States MSHA requirements.  You can read a little more about them at the following link.

http://www.msha.gov/30cfr/18.47.htm

Is this system in the United States?  I’ll also add a link to a white paper that may be helpful.

http://www.startco.ca/library/papers/Ground-Fault Paper.pdf

The paper talks about the selection of neutral-grounding resistors, ground-fault protection for remote mining machines, ground-conductor monitoring, and preferred ground-conductor monitor characteristics.  Page 5 of the paper talks a little bit about Canadian CSA standards and American MSHA standards.

You may be attempting to ground something other than a remote mining machine, but I think this paper contains relevant information with regard to your query.

---
Cory Anderson
http://startco.ca/

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources