Cold Load Pickup Scheme Timers - typical settings?
Cold Load Pickup Scheme Timers - typical settings?
(OP)
Hi all,
I am interested in typical values for the timers in a cold load pickip scheme. Specifically the loss of diversity timer and the timer that retstors the normal protection after restoration.
Thanks!
I am interested in typical values for the timers in a cold load pickip scheme. Specifically the loss of diversity timer and the timer that retstors the normal protection after restoration.
Thanks!






RE: Cold Load Pickup Scheme Timers - typical settings?
Often, the CLPU scheme is asserted after any lock out trip. With older recloser controls it is done manually. I think the last Form 6 I looked at had a 20 second duration setting.
RE: Cold Load Pickup Scheme Timers - typical settings?
RE: Cold Load Pickup Scheme Timers - typical settings?
I.E. shot 0, and 1 (?) torque control the first set of 51 settings.
RE: Cold Load Pickup Scheme Timers - typical settings?
I hope this helps
RE: Cold Load Pickup Scheme Timers - typical settings?
I have only seen one actual recording of cold load pickup, but was very surprised that the load actually continued to rise for several minutes.
RE: Cold Load Pickup Scheme Timers - typical settings?
RE: Cold Load Pickup Scheme Timers - typical settings?