Unit Trafo - Motor with PFC capacitor trips on Differential protection

Unit Trafo - Motor with PFC capacitor trips on Differential protection

(OP)
3.75MW, 11kV Induction motor is connected in 33kV system through a Unit Trafo (33/11kV). There is a capacitor across motor terminals and compensates about 90% of the motor magnetising current. The feeder is tripping on Differential protection. The differential protection covers motor and transformer in its zone but excludes the capacitor. The differential protection is bias type (KBCH130 of AREVA).
Apparently, there is no problem with either the motor or transformer.

Any suggestions!

Thanks.

RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection

This occurs at instant of energization?  

RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection

Hi Raghun.
1. Are you back unit to operation?
2. What is a setting of diff protection?
3. Are you check stabilty of protection again?
4. Are you have DR graph?
5. What is a vector group of XFR?
Please send more information.
Regards.
Slava

RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection

(OP)
dpc,
The info from site is it trips when it is already in service. Do you think if it occurs during starting, it is more readily explainable!

Slavag,
Yes, unit was back in operation.
Differential protection setting, stability, vector group (Dyn1)have been checked and since the equipment is unit transformer connected motor, there is nothing like through fault here.

Thanks to both of you for the responses.

RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection

I'm have a bit of difficulty picturing the arrangement.  Are there two, or three sets of CTs?  If only two sets, how do you exclude the capacitors?  If the capacitors are truly excluded, capacitor inrush, or outrush, could be seen similar to through fault.  If the motor is already running when this happens, outrush is more likely than inrush.  Is there another such combination near by?  If so, does the trip happen when that unit is being energized and the capacitors on both units are ringing against each other?

RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection

Hi.
Raghun, I would like back to my Q:
what is a setting of diff protection.
Not once, XFR diff protection was tripped w/o any reason
after several years of operation. And reson was setting of
I2f blocking and Id> first setting. And problem was not only in energazing of XFR, also in AR on the grid.
I attached this files to Gunnar's thread, but would like attached here too.
Regards.
Slava

RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection

(OP)
davidbeach,

Let me try to clear - the capacitor branch has separate CT which is wired into the differential protection scheme and thus excludes the capacitors from its zone. The motor branch CT is in the motor star point side, where as the capacitor branch CT is at the tap-off.

Thanks.

RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection

Raghun. In additional to David's Q and your's answer:
Capacitor's set CT's are connected  directly to the protection relay ( as 3 win. XFR) or are paralleling wiring with motor's set CT's?
Regards.
Slava

RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection

(OP)
You are right, Slavag. The motor and Capacitor CTs are paralleled externally and connected to the differential relay (Relay type is KBCH120 that is with two bias inputs and not KBCH130). Thanks.

RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection

Rughun.
I'm hope, guys installed same set of Ct's on capacitors and motor.
Regards.
Slava

RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection

Was something nearby being energized when this happened?  Another motor, transformer, cap bank?  I would suspect some type of transient event.  

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close