Unit Trafo - Motor with PFC capacitor trips on Differential protection
Unit Trafo - Motor with PFC capacitor trips on Differential protection
(OP)
3.75MW, 11kV Induction motor is connected in 33kV system through a Unit Trafo (33/11kV). There is a capacitor across motor terminals and compensates about 90% of the motor magnetising current. The feeder is tripping on Differential protection. The differential protection covers motor and transformer in its zone but excludes the capacitor. The differential protection is bias type (KBCH130 of AREVA).
Apparently, there is no problem with either the motor or transformer.
Any suggestions!
Thanks.
Apparently, there is no problem with either the motor or transformer.
Any suggestions!
Thanks.





RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection
RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection
1. Are you back unit to operation?
2. What is a setting of diff protection?
3. Are you check stabilty of protection again?
4. Are you have DR graph?
5. What is a vector group of XFR?
Please send more information.
Regards.
Slava
RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection
The info from site is it trips when it is already in service. Do you think if it occurs during starting, it is more readily explainable!
Slavag,
Yes, unit was back in operation.
Differential protection setting, stability, vector group (Dyn1)have been checked and since the equipment is unit transformer connected motor, there is nothing like through fault here.
Thanks to both of you for the responses.
RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection
RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection
Raghun, I would like back to my Q:
what is a setting of diff protection.
Not once, XFR diff protection was tripped w/o any reason
after several years of operation. And reson was setting of
I2f blocking and Id> first setting. And problem was not only in energazing of XFR, also in AR on the grid.
I attached this files to Gunnar's thread, but would like attached here too.
Regards.
Slava
RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection
RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection
Let me try to clear - the capacitor branch has separate CT which is wired into the differential protection scheme and thus excludes the capacitors from its zone. The motor branch CT is in the motor star point side, where as the capacitor branch CT is at the tap-off.
Thanks.
RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection
Capacitor's set CT's are connected directly to the protection relay ( as 3 win. XFR) or are paralleling wiring with motor's set CT's?
Regards.
Slava
RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection
RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection
I'm hope, guys installed same set of Ct's on capacitors and motor.
Regards.
Slava
RE: Unit Trafo - Motor with PFC capacitor trips on Differential protection