Transformer Impedance Calculation from Test Data

Transformer Impedance Calculation from Test Data

Transformer Impedance Calculation from Test Data

(OP)
Hi,

I'm trying to determine the appropriate way to represent 3-winding Delta transformer to its equivalent Wye representation.  The given data were:  Primary : Secondary voltages, its MVA rating, MW loss, and %Z.  I saw an old note in the past which indicates the calculated resistance as %R = MW loss * 100 / rated MVA.  I didn't see any logic in this resistance calculation.  If you have any links or advices to the above subject, please let me know. Thanks.

RE: Transformer Impedance Calculation from Test Data

The formula you gave is more understandable if you write it as:
%R = I^2 R * 100 / (I^2 Z)

I^2 * R = the resistive losses

I^2 * Z = MVA rating

Expressing the losses as a % of the MVA rating is what the formula does.  It is common to all transformers - be they 2 winding, 3 winding or more.

A test report should give you the %Z between pairs of windings.  With a 3 winding transformer, let's call the terminals H, L and T (high, low and tertiary).

Get 3 values from test report:
Z_H-L = impedance between H and L
Z_H-T = impedance between H and T
Z_L-T = impedance between L and T


Z_H = 1/2 (Z_H-L + Z_H-T - Z_L-T)

Z_L = 1/2 (Z_H-L + Z_L-T - Z_H-T)

Z_H = 1/2 (Z_H-T + Z_L-T - Z_H-L)

Looks better if you can use subscripts, but this should give you what you want.  These impedances, Z_H, Z_L and Z_T are the wye equivalent values.

RE: Transformer Impedance Calculation from Test Data

(OP)
Magoo2,
 
Truly appreciate for your help.  Have a great day.

RE: Transformer Impedance Calculation from Test Data

(OP)
One more question.  What is the difference between the above Delta-Wye conversion and that of the typical formula:  Z_H = (Z_H-L * Z_H-T)/ Z_sum, where Z_sum = Z_H-L + Z_H-T + Z_L-T ?  I'm trying to facilitate the equations above with full representation of Z = R + jX and compare with the one you gave, but have a tough time of seeing the corresponding relationship.  Thanks for any help.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources