Heating Strips
Heating Strips
I work in a compression moulding facility moulding phenolic resin composites. Recently I have noticed that the heater bands in the top and bottom platens of the presses are not all working even though the temperature controller is reading correct. Our setup is 11 bands on both top and bottom platens. I have counted up to 4 bands not working at any given time. How important is it to have all heater bands working? I have worked with extruders before and having all heater bands working is critical but is it the same when heating a platen?
RE: Heating Strips
Do you have a number of temperature controlers or just one for each plattern, ie are all elements in one plattern hooked up to one controller.
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips Fora.
RE: Heating Strips
Our setup on our presses is that we have 3 amp meters each, for both top and bottom platens. The heater bands are connected in the following groups for both top and bottom platens,
Amp Meter 1 - 4 bands connected
Amp Meter 2 - 4 bands connected
Amp meter 3 - 3 bands connected
Yes they do cycle on and off but what I observed was that the amp meters are not pulling enough amps to indicate that all 3 or 4 heater bands are working.
RE: Heating Strips
You will get:
a) Uneven heating across the platens - try spot readings with a surface contact probe.
b) With some heaters off, the others will be working more and this will reduce their life - you will eventually get a "cascade" of failures.
Cheers
Harry