Residual Current Circuit Breakers (RCCBÆs) - Problem
Residual Current Circuit Breakers (RCCBÆs) - Problem
(OP)
We have a stange problem involving RCCB. We have 6 battery chargers connected to a 3ph supply – 240V line to line (2 Chargers on phase 1, 2 chargers on phase 2 and 2 chargers on phase 3 .. All chargers are 240 so we have had to connect them line to line to get the correct voltage, Each charger can pull 3.5kW … We use a 50A 3ph supply.
We have a 30mA RCCB on each phase (htt p://www.ha ger.com.sg /menu/prod uct-offer/ protection -&-con nection/re sidual-cur rent-circu it-breaker s---rccbs- --elcbs/80 0-1483.htm) . The equipment has been working fine in New York. We then move the equipment to Chicago and we now have constant problems with 2 RCCB’s tripping almost immediately. The chargers and cabling is fine, no damage …
Is it possible that the supply (which is obviously upstream of the RCCB’s) can have any influence on a RCCB ?? The only thing that has changed is the electrical supply …from one geographical location to another … My understanding of RCCB’s is that any problem before (upstream) the RCCB’s is irrelevant … it only measures what is downstream ….
Would much appreciate if anyone could put some light on this …
We have a 30mA RCCB on each phase (htt
Is it possible that the supply (which is obviously upstream of the RCCB’s) can have any influence on a RCCB ?? The only thing that has changed is the electrical supply …from one geographical location to another … My understanding of RCCB’s is that any problem before (upstream) the RCCB’s is irrelevant … it only measures what is downstream ….
Would much appreciate if anyone could put some light on this …






RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
Switcher type can have capacitive coupling issues that allow leakage that the RCCDs consider ground faults.
It will likely be something subtle.
Do they run for a while, and then trip, or just flat trip immediately?
Trip when not running?
This is WYE power? There is a neutral you're not using?
Was the power Delta at the prior location?
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
I agree with the capacitive coupling issue with this type of charger. But as I say 4 failing at the same time ??
javascript:openindex(600,400,'/pops/emailthread.cfm?qid=207058&w=600&h=400',1)
E-mail This Thread
We are not using the neutral.
Both installations are supposed to be the same - Neutral not used
Appreciate you comments...
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
How long are the runs now?
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
How is your power quality? If you have a lot more harmonic distortion in the new location that may be affecting the trip elements.
In North America, 240 volt three phase systems are generally delta fed.
The delta may be corner grounded, which will put two phases at 240 volts to ground. The leakage to ground will be higher.
The delta may have be a 4 wire 120/240 single phase-240 volt three phase. If so, the code requires the center point of the 120/240 volt transformer to be grounded. This results in two phases at 120 volts to ground and one "Wild" phase at 208 volts to ground.
The delta may have an artificial neutral to provide a symetrical grounding point. If so, all three phases will have 139 volts to ground.
You may want to see if you can identify the system types in use at both locations.
When the voltages to ground are equal, the 60Hz leakages to ground from each phase tend to cancel rather than returnng through the neutral.
Insulation losses caused by triplen harmonic voltages do not cancel but add on the neutral and pass through the GFI trip unit.
You may want to check that identical GFI breakers are installed at each location.
As Keith says, wire lengths may be significant.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
If I understood your problem correctly,it seems that
1)The RCCBs were supplied at 240 V 3-phase in NY
2)The RCCBs were supplied at 208 V 3-phase in CHICAGO.
Normally these RCCBs are having an intergal electornic circuit with an amplifier which works on a defined voltage range.It takes its control power from the input line side. So there is a possibility that when you feed a lower input voltage (208 V) to the RCCB, the elctronic circuit may trip due to under voltage and shutdown the unit.
Any comments please.
Kiri
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
The cable length from the RCCB to the chargers are the same in both locations. But the equipment is mobile and operate from a extension cable. The length is the about 50ft - 60ft. But the cable is BEFORE the RCCB. The RCCB is mounted on the mobile equipment. It is the RCCB on the equipment that trips. Not in the "building".
The voltage was the same in both locations 240V. That is definite. Waross may have hit on a interesting point. I am also surprised that the cable length may have an influence.
My understanding of the workings of the RCCB that we use is that it compares the current going in each line. If the current is not the same . (The tolerance is 30mA) It assumes that the current must have gone to ground and the unit trips.
We are now moving the equipment to California. Will know next week if we have the same problem at the new location !
Any further comments or suggestions are highly apreciated
Have a good weekend !
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
You won't have any problems in California, our electrons, like the weather, are much better behaved.
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
I'm not so work with RCCB, but in our area RCCB used in all
LV application exclude UPS connection. Same RCCB ( different companies, SIEMENS, Hager, ABB, MG, etc.) with 30mA range. I never heard about any influence of cable lenght on the RCCB operation.
You are right, priciple of operation of RCCB it's eql. between in and out current, that means problem is possible only into your mobile eq. BUT we assume that your eq are O.K.
What I can recommend:
1. Check leakedge current.
2. Try put with 30mA RCCB in series 50mA and 100mA RCCB and check what will happened.
I'm also not sure if voltages 110V or 208V or 240V can influence on the RCCB operation.
BUT, I think, grounding type of supply (TNC, TNN, TN-C-S)
must be influence on the level of leakedge.
I think, Bill excplained it as well.
Regards.
Slava
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
You realize that if you hooked a resistor between the hot and the safety ground wire you would get a current imbalance that if sufficient would reach 30mA and trip the RCCB right? Of course, that's the whole point.
So if you hooked a capacitor up instead of a resistor since this is an AC system you could achieve the same tripped result. Most every AC wiring system has the HOT in close proximity to a safety ground, whether it's a metallic conduit, or the associated safety ground traveling along with the hot. Hence a capacitance/foot(meter).
So, if the wire run after the RCCB gets long enough you will almost always reach 30mA of leakage, sooner, or later. Sooner, if the cable/wiring has higher capacitance, later if it is lower.
We have a lot of conversations here about faulty, flaky, safety circuits for long systems like conveyors where you can't even use AC in the circuit because the capacitance is enough to cause malfunctions.
That's why you have to ask about length.
Now if the RCCBs are on the equipment.. That likely isn't the problem, agreed!
So what does that leave? Hmmm. Not sure. Switchers often have front end filters that can have capacitors to ground. I had a computer with the standard LC filter puck. The ground was not connected to the case of the filter. The capacitors in the filter 'leaked' to the computer chassis. It would nail you if you touched it.
It could be you had higher safety ground resistance before and the equipment's leakage was 29mA(all the time), now here with a lower ground resistance it just tips over the edge. Perhaps you could put an ammeter in the ground return to see just what's happening. Any chance before the equipment was isolated from ground and now it isn't? Like it was on rubber wheels and now it sits on concrete?
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
I think Bill's coment about the earth (TNC, TNN, TN-C-S) sound to me the most plausible reason for the problem.
Can someone explain the abbreviations please
TNC
TNN
TN-C-S
Thanks
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
I was typing my reply before I had seen your reply... The equipment is actually on rubber wheels... I will see if I can get our service engineer to check the ground connection with a clamp on current tester. The ground connection is via the extension cable - We use no separate ground spike/rod
The wire installation - After the RCCB is a standard wire harness we have used for a few years here in Europe, and we have not had RCCB trips that we could not explain (water in electrical boxes or loose connections etc.. I can understand)
But this is first time we have had the equipment working in the US ... so I think that it may be an "upstream" problem. Will be very interesting to see if the "electrons" in California is any better..
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
Please see attached:
thread238-201637: 3 Pole vs 4 Pole Circuit Breaker Usage
you will found usefull information.
Keith, I need think about your point, on this moment I haven't any opinion.
Regards.
Slava
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
Claver, what do you mean: neutral not used?
Could you please send us some scheme of internal connection.
Regards.
Slava
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
Good Luck in California
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
Have a good weekend !!
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
However harmonic distortion on the supply system may have an effect on GFIs.
Uneven voltages to ground that may occur with different systems may have an effect on GFIs.
Another possible cause is that you do have ground leakage in your chargers but there was a bad ground connection somewhere in the system that was not allowing leakage current to flow and trip the breaker. If you then moved to a location with good quality grounding the breaker would then trip.
A quick test that we should have mentioned earlier is to "roll"the chargers. Move the chargers on phase "A" to phase "B". move the chargers on phase "B" to phase "C" and move the chargers on phase "C" to phase "A".
If the same breakers trip, measure the voltages to ground. Look for a supply problem.
If different breakers now trip check the chargers that cause the trip.
Please do this simple test and report back to us, and we may be able to help you further.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
I have just received email that our equipment have arrived in California ... Will check on Monday and let you all know the outcome. The 8 hour time difference makes it all a bit difficult.
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
I read several documents on the topic and start understand, that possible also other problem. In Claverh's scheme RCCB's are protected on chargers. Possible DC components in the residual current. I surprised to know , that possible order several types of RCCB's. please see attached document.
Maybe this type of RCCB not applicable to this scheme.
Best Regards.
Slava
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
"To prevent nuisance tripping all the RCCB's are protected against transient voltages (lightning, line disturbances) and transient currents (from high capacitive circuits). RCCB's Type A for DC-pulsating faults or time delay devices are available, please consult us."
Regards.
Slava
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
Though that is most definitely not what I'm referring to.
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
We have made no change to the equipment ...Same extension cable.. The supply we are connected to now is in a new building.
So it looks clear that the SUPPLY (upstream) was the problem ....
Have a great weekend !
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
Probably as waross and others said that the harmonics were a problem at your previous location.
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
Not only electrons are better, I'm hope, weather is better too.
Claver , thank you for the feed back.
Regards.
Slava
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
On the question of Harmonics ... This is outside my expertise, Can you "measure" this ? I am concerned if we ship the gear to another part US and have similar problems... I was even thinking about removing the RCCB.... Not a good idea for safety I know... So that is not really an option...
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
A neutral-to-earth connection downstream from the RCCB would result in healthy single phase current returning to the source via the earth conductor which is external to the RCCB toroid CT, this would be seen by the RCCB as earthfault current. Conversley an earthfault would result in some of the earthfault current returning to the source via the neutral conductor, this would result in the RCCB sensing an earthfault current lower than the actual earthfault current.
The three phase conductors plus neutral must pass through the toroid CT. Slavag's attached file demonstrates the required connection.
RE: Residual Current Circuit Breakers (RCCBÆs) - Problem
For more detailed investigation I use a Fluke 433 which has been replaced by the Fluke 434. This gives a measurement of each fundamental frequency out to the 51st fundamental.