SSR and two speed AC motor

SSR and two speed AC motor

SSR and two speed AC motor

(OP)
I am using an SSR to start/stop a two speed 230VAC motor from a computer. The motor has 3 wires (neutral, low speed and high speed). When the high speed wire is connected to the SSR it works as it should. When the low speed wire is connected the motor will not stop. The motor draws around 50mA which is in the load current range of the SSR. What is the cause for this and is there an easy fix? I guess it has to do with zero crossing, or....

RE: SSR and two speed AC motor

50mA is pretty small.  Try a .22 or .47uF across the motor supply lines.

RE: SSR and two speed AC motor

A  small SSR is probably triac-based rather than antiparallel thryristors as would be found on a bigger type. Under some load conditions the triac won't recover a blocking state after the current zero crossing before being forward biased again. This is inherent in triacs, which conduct twice per mains cycle unlike a thyristor which conducts once per mains cycle.

Easy fix... find a thyristor-based SSR designed for inductive duty.
 
 

----------------------------------
  
If we learn from our mistakes I'm getting a great education!

RE: SSR and two speed AC motor

(OP)
I use a Crydom DPA6111 and the data sheet claims it has SCR output. Will try a capacitor across the motor supply lines as suggested.

RE: SSR and two speed AC motor

I wouldn't put a cap across an SCR...

RE: SSR and two speed AC motor

(OP)
A 0.33uF in parallel with the load (motor) solved the problem. Thank you.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources