Resistance Coefficient, K
I am trying to determine the resistance coefficient, K, of a single-offset, butterfly style damper. Since, there is no readily available data for dampers I was going to utilize the K values of butterfly valves. Unfortunately, the formulas available are limited to sizes below that which I am looking for.
On page A-29 of Crane Technical Paper No. 410, they list formulas for determining the K value for butterfly valves of sizes 2 to 8", 10 to 14" and 16 to 24". The formulas are K = 45 ft, 35 ft and 25 ft respectively, where ft is the friction factor in a zone of complete turbulence.
The dampers that I need to determine the K values for for 8 sizes up to and including 84".
The following link shows that the K value of a butterfly valve decreases as the diameter increases.
http://www .westerndy namics.com /Download/ friclossfi ttings.pdf
However, some tables that I have for "Sizing Coefficients of Rotary-Shaft Valve Bodies" show a Kc value (which I am assuming is the resistance coefficient) of 0.26 for "rotary-eccentric disc" and 0.25 "butterfly-conventional disc" under a heading of "Valve and Trim Style" for 90 degrees of valve opening. Unfortunately I do not know the source of these tables.
I was hoping someone might be able to help clear my confusion and provide some answers. Your help would be greatly appreciated.
http://www
RE: Resistance Coefficient, K
If you have the Cv value you can calculate the K value from K=891*d^4/(Cv^2) (see Crane page 3.4).
One section (Section 9) in this publication gives resistance coefficients ("K" values) for various openings of dampers in pipe and rectangular ducts. Another section (Section 10) treats obstructions of various shapes in pipe or rectanular ducts. You might have to use both sections of the publication to estimate the resistance for wide open (obstruction) versus partial opening.