Relieving capacity of PRV

Relieving capacity of PRV

Relieving capacity of PRV

(OP)
Hi

In the following equation
A=(13160W?TZ) / CKP1Kb?M

A =    Minium effective discharge area,square millimters                                    
C=     Coefficent determined from an expression of the specific heats of gas or vapour at standard condtions (if not known use 315)                                        
K=    Effective coefficent of discharge K= 0.975                                        
Kb=     Capacity correction factor due to back pressure = 1 for atmospheric                                        
M=     Molecular weight of the gas or vapour from standard tables                                         
P1=     Reliveing pressure, KiloPascals absolute. This is the set pressure (kPa) + overpressure (kPa) + atmospheric pressure (kPaa)                                        
T=    Absolute temperature at the valve inlet, degrees Kelvin (C + 273)                                        
W=     Relieving capacity, Kilograms per hour                                        
Z=     Compressablity factor. Use Z = 1.0 if value unknown                                        
What would W relate to ? a % of tank volume?

Thanks

RE: Relieving capacity of PRV

W is the required relieving flowrate (at relief conditions) established from an overpressure scenario analysis.

RE: Relieving capacity of PRV

(OP)
Thanks I have just found that myself.

Is A - Minimum effective discharge area,square millimeters                                    

The area of the flange on tank or exit erea of PRV?

RE: Relieving capacity of PRV

A is in mm's.  It is the relief valve orifice area.  Check out API 526 for relief valve body sizes vis-a-vis orifice size.

RE: Relieving capacity of PRV

About A

The way i understood it A is actually more like a nominal area that makes it possible to compare valves from different makers. Ther actual free area may differ but the manufactor will then know how to compensate.

Best regards

Morten

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources