VFD, Active Harmonic Filter, Power Consumption???

VFD, Active Harmonic Filter, Power Consumption???

RE: VFD, Active Harmonic Filter, Power Consumption???

What page are you looking at?

RE: VFD, Active Harmonic Filter, Power Consumption???

(OP)
Product Specification page 7.

RE: VFD, Active Harmonic Filter, Power Consumption???

A 50A rated unit in a NEMA 1 housing operating at rated current will dissipate 1800W of losses as heat.

A 50A rated type in a NEMA 12 housing operating at rated current will dissipate 2150W of losses as heat.
 

----------------------------------
  
If we learn from our mistakes I'm getting a great education!

RE: VFD, Active Harmonic Filter, Power Consumption???

(OP)
I can read that much.  Doesn't that mean I am using from 7% to 9% more energy?

RE: VFD, Active Harmonic Filter, Power Consumption???

No, it means that of the energy going in, that much is being lost as heat.

By the way, measure the heat loss across a restricted valve. Most of it is carries away in the fluid, but that energy is still lost, and it has to come from somewhere.

RE: VFD, Active Harmonic Filter, Power Consumption???

(OP)
"No, it means that of the energy going in, that much is being lost as heat."

So to control the harmonics from a 50 amp motor, the active harmonic filter is losing 2150 watts to heat.  Isn't that adding another 2.88 HP load to the system?

RE: VFD, Active Harmonic Filter, Power Consumption???

Yes, well sort of...

IF you have decided that harmonic mitigation is important to you and have decided to use a device such as that, then of the 50A going through it, up to 2150W of that energy will be lost as heat.

BUT (and this is a BIG BUT wink) a 50A Active Filter is not used for a 50A motor, the 50A refers to handling 50A of harmonic current, not 50A of load current. 50a of harmonic current would imply a much much bigger motor; probably in the range of 300-400HP (assuming 460V). So that "2.88HP" of losses becomes somewhat insignificant compared to the potential energy savings of using a VFD compared to throttling. As I said, think about the energy loss across a valve on a 350HP pump. Probably more than that, and all that energy had to come from the pump motor. I'm not an ME, but I'd bet it is a wash at best...

http://www1.eere.energy.gov/industry/bestpractices/pdfs/control_valves_pumping_ts10.pdf

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources