bacon4life
Electrical
- Feb 4, 2004
- 1,531
What it the typical accuracy of relaying CT's at typical load values of 0.1 to 1.0? I am asking because I just tried to add up the MW & MVAR at one our buses with c400 & c800 CT's feeding panel meters. The net MVA at the bus was about 7% of the total flowing through all the lines. What suprised me was variation in the total for each phase was much less than the unbalanced currents between the phases. I guess it is really two questions.
1. For a set of identical CT's, will they normally read the same value within say, 1%.
2. In comparing two different sets of relaying CT's, how much error should I expect?
I know IEEE C57.13 defines worst case accuracy as +/-10% between 1.0 and 20 times full load, but it doesn't address less than 1.0 PU loading, nor would it address typical nominal values.
Thanks
1. For a set of identical CT's, will they normally read the same value within say, 1%.
2. In comparing two different sets of relaying CT's, how much error should I expect?
I know IEEE C57.13 defines worst case accuracy as +/-10% between 1.0 and 20 times full load, but it doesn't address less than 1.0 PU loading, nor would it address typical nominal values.
Thanks