Earthing lightning arrester

Earthing lightning arrester

Earthing lightning arrester

(OP)
Dear friends,
please advice regarding method of earthing LA at distribution line. In our current practice 13.8 kV line with using pipe pole, the LA is always earthed to gound via pole (brazed), but our new study shown that the earthing of LA must be via a special wire to reduce impact of surge impedance at pole.

Is it realistic??

RE: Earthing lightning arrester

To earth the LA via a separate conductor is not only realistic but also adivisable.  the LA should be effectively earthed to ensure its function Actually  our practice in small substations is to provide a separate earthpit.. but on line earth cable with proper earth & min resi. is OK

RE: Earthing lightning arrester

It is realistic.  A surge event or lightning strike can be visualized as a massive build-up of electrons trying to get to ground in a big hurry.  If they have a direct, low-impedance path, this is where the bulk of the current will flow.  If the path is high impedance or has a lot of bends and convolutions, the current will find additional pathways.

This surge current has high frequency components and the added inductance of a steel conductor will present a high impedance.

RE: Earthing lightning arrester

(OP)
Thanks friends.

Actually our pole design is using pipe pole, and static wire is barecooper 35 mm.

If we consider that the impedance of barecooper is lower than pipe, this method is okey, otherwise...

RE: Earthing lightning arrester

Yes, but how does the static wire get to the earth?  You will want a direct copper connection to earth at each pole for the best protection.

RE: Earthing lightning arrester

(OP)
I mean that the bare cooper (same wire for static) is used to connect the bottom of LA to ground.

For certain pole, we also ground the static in order to get lower system impedance.

RE: Earthing lightning arrester

2f4n, if you haven't done so, you may want to look over 'Subscribe To Forums' and 'Personal Profile' links in the upper lefthand corner of most of the Eng-Tips pages.  It's kind of a busy place.
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources