VFD voltage dip consideration
2

VFD voltage dip consideration

VFD voltage dip consideration

(OP)
I'm running a generator sizing program and I have two VFD's (15 hp and 20 hp).  I can select each of these for up to 25% permitted voltage dip (to reduce the size of the generator), but now I'm having trouble finding VFD's with greater than 10% permitted voltage dip.  Any suggestions?
Thanks and have a happy new year!!
-J

RE: VFD voltage dip consideration

Drives built for the international market will have a much broader input voltage range.  For example, ABB's 460V class drives are good from 380 -10% to 500 + 10%.  Other brands are out there that do the same.

RE: VFD voltage dip consideration

What do you define as a voltage dip? there is a difference regarding the tolerance defined by a VFD, typically +/-10% of 380~480(or higher)Vac and the capability of a VFD to cope with a power dip (sag). If it is ms or secs or minutes or constant then it will have a large impact on the VFD design.
Most VFD's will have an undervoltage trip limit way below the level shown in the voltage tolerance, but it will be time dependant.
If you are looking for power ride through then this can be defined for a short period of time but if you are looking for a VFD to operate at a lower voltage than the nominal over a long period of time then this will not only push the current demand in the VFD but screw up the motor you are connected to. You can only provide a maximum output subject to the input.

RE: VFD voltage dip consideration

(OP)
oz, thanks for the reply.  I'm talking about what the VFD can handle in the electrical system.  Specifically, there's a chiller with two 50hp (non-VFD) compressors.  during generator operation, when these compressors start the voltage will dip as the generator controls compensate.  I wanted to see how other folks dealt with the issue.
With further investigation on the side, I was able to figure that the only time I had a problem was when the entire building came on as a block load... by staggering the AHU and chilled water components on initial start up via the BAS, I was able to keep VD below 10%.

Thanks Dick and oz!
-John

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources