TRANSFORMER TAP RATIOS

TRANSFORMER TAP RATIOS

TRANSFORMER TAP RATIOS

(OP)
Does anyone know how the primary taps ratio on a transformer work.  Is a +2.5% tap apply to the full voltage accros the primary or to the number of turns on the primary?  To raise the secondary voltage does one connect to the + or the (-) taps?

RE: TRANSFORMER TAP RATIOS

The tap value is the % change in the number of primary turns.  A +2.5% primary tap means that for a primary voltage 2.5% higher than the nominal, the secondary no-load voltage will be at nominal.  To raise the secondary voltage, lower the primary tap.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources