I would like to test the mV drop of a mated connector. What is the best method to do so. The connector is supposed to be rated at 200A.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: mV drop testing?
ht
Basically you would put about 100 A to 200 A through it and measure the voltage drop.
RE: mV drop testing?
What access do you have to test equipment? Are you in the test lab of a major organisation, or playing with this on the dining room table? It helps to know roughly what level of resources you have access to.
A 200A DC source should be fairly easy to hire, or you could make a simple AC source yourself. Use a couple of turns of heavy cable passed through a toroidal transformer core and close the loop through the connector. Leave the original secondary open circuit. A variac would be a useful way to control the primary voltage, thus allowing you to regulate the current. There should be virtually no reactive component of the connector impedance so the measurement should be simple enough without worrying about complex impedances: R=V/I.
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: mV drop testing?
http://www.amperis.com/productos/ohmimetros/
Nowadays there are ohmmeters that use bateries and are portable, if you get a good ducter you may not need to inject higher currents than 10 A.
So, once you meter the resistance, to calculate the voltage drop you just need to muliply the current thru times the resistance. The resistance is independent from the value of the current.