Hi everyone

I have a UPS system that goes that way:

Inverter:
600V-120/208V transformer 3 wires going through a 3 pole breaker that makes the input of the UPS.

bypass:
600V-120/208V transformer 4 wire going through a 3 pole breaker that makes the input of the bypass. The neutral is not going through the breaker.

The bypass neutral is what that makes the neutral of the inverter at the output of the UPS.

My question: Does the neutral have to go through the breaker (4 pole breaker)?

I do know that the neutral cannot be wired alone and must be included into the 3 phase wire.

Thanks!

RE: Neutral in a UPS setup

The neutral should not go through the breaker. Otherwise the UPS output will loose its ground reference if the breaker opens.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources